securespark said:It's just that some instructions are written by monkeys. They're not fit to wipe your @rse on..
Who's shower was it anyway? Give me the details and I'll ring em up & give em some stick...I like that sort of challenge!
Mira Showers said:To obtain full advantage of the power provided by this unit, use the shortest
possible cable route from the consumer unit to the shower. It is also necessary
to satisfy the disconnection time and thermal constraints which mean that, for any
given combination of current demand, voltage drop and cable size, there is a
maximum permissible length of circuit.
As a guide only, the following maximum permissible lengths are given for
6 mm2 and 10mm2 cable protected by a 45A MCB type B and allowing for a 5
volt drop:
Mira Sport 10.8 kW (240 V AC) at 240 V - 15 metres 6 mm cable
Mira Sport 10.8 kW (240 V AC) at 240 V - 25 metres 10 mm cable
plugwash said:im sure it came up a while ago on here that burried directly in a normal (non insulateing) wall was installation method one (same as clipping direct)
can any sparkysconfirm this?
securespark said:Hmmmmmmmm.