Indeed, you cite the two possible valid reasons for a 4mm² ring that I mentioned.I don't get what all the issue is about, a 4mm ring is pretty common in commericial work, and while there was probably no need to go to 4mm in the OPs case, its not wrong to do so. .... Volt drop is often the reason they are specified, but often very cautious design assumptions are made, such as assuming the loading is 20A in the middle of a ring and then extra 5A load at 1/4 and 3/4 around. When the acutal load is a couple of PCs and less than 5A...... Grouping factors are another thing that might result in 4mm rings
As you say, that could be an issue with a C32, but I think probably pretty unlikely with a B32, since (if I've done my sums right!) Zs would then only become a problem before a "5% VD" one did if Ze were greater than about 0.72Ω, which is probably pretty unlikely in a TN installation.Might also be necessary to meet Zs on longer rings, espeically with C type MCBs and no RCD
I think you've probably misunderstood. When he wrote ...If you've used 2 core and you don't earth the armour, will your new sockets have no earth, or have I missed something
... I took that he meant that he was using 3-core, and therefore "not using the armour as the earth as one would if it were 2-core"..... the armour!! its stripped back completely from the terminals and is not used as the earth as in 2 core.
I'm not quite sure what you mean by 'technical standard' (that's what BS7671 is) but, yes, virtually everything in BS7671 relates to 'safety', in one sense or another.Safety is the most important technical standard in BS7671.
Post a picture of the swa entering a socketis anyone happy to give me a thumbs up on what i have proposed (almost finished) ??
Still need to earth the armouring regardlessI think you've probably misunderstood. When he wrote ...
... I took that he meant that he was using 3-core, and therefore "not using the armour as the earth as one would if it were 2-core".
Kind Regards, Joh
So, let`s say I`m using three core SWA. so I have L, N & E conductors. I have used stuffing glands rather than SWA glands at the ends. Would I need to make an earthed connection to the SWA armour in every conceivable instance then ?Still need to earth the armouring regardless
I would say yes, as it's an exposed conducive part, but in the OP's case it's not going to be exposed, so bit of a grey area in my opinionSo, let`s say I`m using three core SWA. so I have L, N & E conductors. I have used stuffing glands rather than SWA glands at the ends. Would I need to make an earthed connection to the SWA armour in every conceivable instance then ?
We went through this at length recently.Still need to earth the armouring regardless
Yes, as you will presumably realise, that is also my view. However, I can see no harm in earthing it - one doesn't even have the usual argument that 'unnecessarily' earthing something is undesirable, since the armour is not even touchable (if the cable is intact)Surely it is quite clear that if the armour is being used as electrical protection (and/or as a reason not to fit an RCD) then it must be earthed. If used only as mechanical protection, then it does not require earthing.
Well, it certainly can't be an "exposed-c-p" if it's not exposed!It is only an exposed-conductive-part if left exposed where live connections might become loose.
I'm not sure I understand. I have not said anything about (nor even considered to much of an extent) anything 'becoming loose'.Agreed - but you seem to be counter arguing "if left exposed where live connections might become loose" with examples of "exposed or not exposed with no connections likely to become loose".