In a new build, we have a 9.5kw Mira shower connected to the consumer unit via a 40amp MCB and what looks like 6mm cable.
When we use the shower the MCB in the consumer unit makes a buzzing noise.
The builders have sent out an electrician to look at this three times now. The first time they tightened a loose cable, the second time they said the MCB would need replacing, and they third time they replaced the MCB. The buzzing still remains. On the final visit, the electrician said the shower must be faulty, and we needed a plumber.
The buzzing stops when you switch the shower onto it's lowest setting.
Today a plumber has been out and pointed out that he thinks the cable should be 10mm and not 6mm for a 9.5k shower.
Before I go back to the builder and ask them to arrange for a new lower power shower to be fitted, is the plumber correct?
When we use the shower the MCB in the consumer unit makes a buzzing noise.
The builders have sent out an electrician to look at this three times now. The first time they tightened a loose cable, the second time they said the MCB would need replacing, and they third time they replaced the MCB. The buzzing still remains. On the final visit, the electrician said the shower must be faulty, and we needed a plumber.
The buzzing stops when you switch the shower onto it's lowest setting.
Today a plumber has been out and pointed out that he thinks the cable should be 10mm and not 6mm for a 9.5k shower.
Before I go back to the builder and ask them to arrange for a new lower power shower to be fitted, is the plumber correct?