I'd be grateful if a practising electrician could help answer a few questions about wiring regulations, as I'm suspecting I've been considerably 'short-changed' on an electrical installation and want to get the facts straight before taking any action.
I have a large wooden outbuilding and recently had the domestic consumer unit upgraded as part of a professional installation to supply mains power to the outbuilding.
My original specifications for the installation were:
30A (min) supply, 40A if possible
Buried 10mm2 SWA twin and Earth
Total run from consumer unit to workshop termination: 15.5m
In-case it's relevant, I should add that the electricity meter is rated at 80A max.
I confirmed the specs with the engineer a couple of days before installation. However, he turned up with SWA cable clearly smaller than the 10mm2 we had agreed. I was informed that this was 4mm2 (passable I suppose for a 30A feed) but a visiting colleague reckons it is looks like 2.5mm2. Reluctantly, I accepted 4mm2 as I had booked a day off work and had further work scheduled the following day (requiring power to the workshop).
I was informed that it was not permitted for SWA cable to be routed into the house so conventional 2.5mm2 ring-mains cable was connected and routed inside wall-mounted PVC trunking the few metres from the outside wall to the CU in the kitchen cuppboard. Immediately I questioned this as I thought it was under-rated for 30A but was infomed that he could only give me a 16A-fused supply.
Question 1: Should approved SWA mains cables carry some BS or rating indication, as there's nothing on the black outer sleeve?
Question 2: As it is buried and routed in PVC conduit, what would be the maximum safe current for 2.5mm2 (assuming worst-case cable specs due to lack of type markings, etc).
Question 3: Is there some regulation limit on the maximum permissible supply current to wooden outbuildings, or could this be limited by the 80A-max electricity meter? Could the 16A fused supply have been to suit cheap/under-rated cable to the cost and convenience benefits of the installer - obviously at my cost?
Thanks in advance.
FJ
I have a large wooden outbuilding and recently had the domestic consumer unit upgraded as part of a professional installation to supply mains power to the outbuilding.
My original specifications for the installation were:
30A (min) supply, 40A if possible
Buried 10mm2 SWA twin and Earth
Total run from consumer unit to workshop termination: 15.5m
In-case it's relevant, I should add that the electricity meter is rated at 80A max.
I confirmed the specs with the engineer a couple of days before installation. However, he turned up with SWA cable clearly smaller than the 10mm2 we had agreed. I was informed that this was 4mm2 (passable I suppose for a 30A feed) but a visiting colleague reckons it is looks like 2.5mm2. Reluctantly, I accepted 4mm2 as I had booked a day off work and had further work scheduled the following day (requiring power to the workshop).
I was informed that it was not permitted for SWA cable to be routed into the house so conventional 2.5mm2 ring-mains cable was connected and routed inside wall-mounted PVC trunking the few metres from the outside wall to the CU in the kitchen cuppboard. Immediately I questioned this as I thought it was under-rated for 30A but was infomed that he could only give me a 16A-fused supply.
Question 1: Should approved SWA mains cables carry some BS or rating indication, as there's nothing on the black outer sleeve?
Question 2: As it is buried and routed in PVC conduit, what would be the maximum safe current for 2.5mm2 (assuming worst-case cable specs due to lack of type markings, etc).
Question 3: Is there some regulation limit on the maximum permissible supply current to wooden outbuildings, or could this be limited by the 80A-max electricity meter? Could the 16A fused supply have been to suit cheap/under-rated cable to the cost and convenience benefits of the installer - obviously at my cost?
Thanks in advance.