What if you increase the cable size?A spur from a ring at any point can only have one socket
What if you increase the cable size?A spur from a ring at any point can only have one socket
A spur from a ring at any point can only have one socket attached. If this is a double socket, the maximum load is 2x13amps.
Obviously the capacity of one 2.5mm² cable is less than two 2.5mm² cables.Since the spur is a radial using 2.5mm cable, isn't its capacity less than a ring in 2.5mm as the load is distributed across the two legs of the ring?
Not particularly because of the joint required; but because it is unnecessary.Are you averse to the ring extension (when there is a need for multiple new sockets) because of the join it requires?
I think it is called common sense - a rarity these days.Trying to understand the reasoning.
Of course. Why do you even have to ask?Can I also clarify, are you suggesting that a spur from any point on the ring (and in this case the MCB) could be for more than one socket if you increase the cable size?
Think about the rule for an FCU.And it no longer requires an FCU at the start of the radial?
As said, that is not mentioned in the regulations for some reason.What if you increase the cable size?
Because of this comment:Of course. Why do you even have to ask?
A spur from a ring at any point can only have one socket attached
good!According to the regulations; you may have a 2.5mm² spur to one socket (ignore double sockets for the moment); the cable has a capacity of 27A (yes, method C) but the plug fuse limits the current to 13A - all good.
I know you suggested we ignore them but is the above true for two single sockets and a double socket? Do they both limit the current to 26A?You need another socket so you extend the spur; now you have a 27A cable, two sockets/plugs which limit the current to 26A - all good.
But...the cable is rated at 27A and the two sockets will pull 26A and therefore not exceed the capacity of the cable. Isn't it the third socket that warrants the FCU as that potentially takes you above the capacity of the cable (if all sockets are maxed at 13amp each)?But now for some reason the regulations (sort of) say you must have at the source a 13A FCU. This is because that is all that is available and the lack of a suitable accessory; i.e. a 25A(27A) FCU.
Fair enough.Because of this comment:
Yes, they do but two single sockets is not allowed (according to some).I know you suggested we ignore them but is the above true for two single sockets and a double socket? Do they both limit the current to 26A?
True - so it should be allowed - or is - depending on how the regulations are interpreted.But...the cable is rated at 27A and the two sockets will pull 26A and therefore not exceed the capacity of the cable.
Yes, of course, but don't you agree that that is a daft way of making things safe? Use larger cable or larger fuse (in something other than an FCU).Isn't it the third socket that warrants the FCU as that potentially takes you above the capacity of the cable (if all sockets are maxed at 13amp each)?
I would point out that such a rule would negate or contravene the regulations relating to the positioning (or indeed omission) of overcurrent protection devices which actually do allow two single sockets on a 2.5mm² spur from a 32A circuit.If, like some, one is worried about future idiots then why not specify that 4mm² must be used for all spurs. Simples.
Yes, if I could be bothered. But, quite honestly, @Jupiter01 has been playing at electrical stuff for many years.What TTC should have written is "A spur from a ring at any point can only have one socket attached - if it is 2.5mm² according to one way of reading of the regulations"
We've been through this umpteen times, and there is no clear generic answer.Total 20amps on a twin socket.
When I asked, even the technical guys at MK were not able to tell me what that is meant to mean (because, I was told, "Technical Data Sheets" were written by the marketing dept.!) but it surely can only be interpreted (for a double socket) as either 13A (total) or 26A (total), not 20A?
Indeed. But, should someone do this, then the load on the 2.5mm spur will still be inside the rated spec of 27amp*I thought I saw some marked in the moulding 'MAX 20amp), but then - why would anyone need two 3kw loads co-located?
I don't personally recall ever having seen that, but maybe you did - as I said, there is nothing stopping a manufacturer producing a double socket which only 'just' satisfies the minimum requirement of BS1263, hence presumably would have to 'rate' it at 20A.I thought I saw some marked in the moulding 'MAX 20amp) ....
Very unlikely, I agree, but not impossible., but then - why would anyone need two 3kw loads co-located?
Quite so, but ....Indeed. But, should someone do this, then the load on the 2.5mm spur will still be inside the rated spec of 27amp*
Maybe the person(s) who invented Appendix 15 had it in their mind(s) that 433.1.204's minimum requirement of a CCC or 20A for the cable of a ring final circuit also applied to the cable of an unfused spur, such that it might not be adequate for 26A, but would be adequate for what they regarded (as seemingly other do) as being the (20A) 'rating' of a double socket - hence their guidance that an unfused 2.5mm spur could supply one double socket but not two single ones (which I don't think anyone disputes would each be 'rated' at 13A)?* installation method permitting.