Plug & FCU fuses Come in 1, 3, 5, 7, 10, & 13 amp ranges,
But only the 3, 5, & 13 amp fuses are commonly available,
I think "RS" still supply the 1, 7, & 10 amp,
As a heater is very unlikely to fault to a marginal overload, rather than catastrophic short, and assuming the feed cable will be up to it, a 13A fuse will be fine in practice, and avoids problems with cold inrush (not that i'd expect much from a storage heater, as the absolute temperature range isn't that great.)
Actually a typical 5 A fuse will never reliably blow at 5.4 amps, but it will dissipate over a watt, and probably oxidise and burn its contacts over time.
As an aside this is a serious problem with some designs of cheaper moulded plug, as the heat can't get out and when people have fitted the lower rated fuse 'to make things safer' they actually introduce a greater risk.
The regs do specifically say that the over current protection need not be a close fit for fixed heaters and immersions, though without the book here now I can't quote you a page number or the form of words.
Thanks for that, I knew the heater was closer to 5A and that was what was confusing me as the 13A fuse seemed so much larger. Hadn't seen 7A or 10A fuses but will try those places and use one of them.
Cheers
Thanks for that, I knew the heater was closer to 5A and that was what was confusing me as the 13A fuse seemed so much larger. Hadn't seen 7A or 10A fuses but will try those places and use one of them.
Cheers
If you need to find a tradesperson to get your job done, please try our local search below,
or if you are doing it yourself you can find suppliers local to you.
Select the supplier or trade you require, enter your location to begin your search.
Please select a service and enter a location to continue...
Are you a trade or supplier? You can create your listing free at DIYnot Local