Just looking to find out where to select 't' the disconnection time for the Adiabatic formula. (This is for college not an actual install.)
Using an EN60898 breaker, 16A. Type B.
Do I look up a datasheet for the breaker?
Do I use table 41.1 in the regs book? Part of regulation 411.3.2.2 (0.4 seconds for a TN system, 230V AC)
Do I assume 0.1 seconds given the range 0.1 to 5 seconds in Fig 3A4 in the regs book?
Please explain which to use. The regs book just says 't' is the operating time of the protective device with 'I' amps fault current. It doesn't say typical, minimum or maximum.
I'd like an answer suitable for C&G exams rather than "I always use blah blah", ideally refering to something in the regs book!
Cheers!
EDIT: I think that there is no specific regulation I can refer to. With a fault current in excess of 5x the rating, the breaker operates in a few milliseconds, so using the 0.1s figure is still very conservative.
Using an EN60898 breaker, 16A. Type B.
Do I look up a datasheet for the breaker?
Do I use table 41.1 in the regs book? Part of regulation 411.3.2.2 (0.4 seconds for a TN system, 230V AC)
Do I assume 0.1 seconds given the range 0.1 to 5 seconds in Fig 3A4 in the regs book?
Please explain which to use. The regs book just says 't' is the operating time of the protective device with 'I' amps fault current. It doesn't say typical, minimum or maximum.
I'd like an answer suitable for C&G exams rather than "I always use blah blah", ideally refering to something in the regs book!
Cheers!
EDIT: I think that there is no specific regulation I can refer to. With a fault current in excess of 5x the rating, the breaker operates in a few milliseconds, so using the 0.1s figure is still very conservative.