Or does it mean that unless you put 8 conductors (3 x 2.5mm², 3 x 4mm² & 2 x 6mm²) into the terminals you are not complying?Re: Chief Devil's Advocate
Applying logic to the assumption that the above is considered to be 'manufacturer's instructions' and not following them would render the installation non-compliant.Terminal capacity:
Live, neutral & earth
3 x 2.5mm2
3 x 4mm2
2 x 6mm2 (stranded)
Only one, only two or four 2.5mm² conductors would be non-compliant.
Only one or only two 4mm² conductors would be non-compliant.
Only one 6mm² conductors would be non-compliant.