This system gets more perplexing every day! Running HW alone allows the boiler to operate over a reasonable temperature range: 52C/72C. Running one rad only is similar: 47C/70C. Running two rads drops it to 41C/52C. I was running a Wilo Gold RS50 at speed 3.
I renewed the pump to an RS60 (yes, I know it's overkill!)
Running at speed 2 with two rads, boiler runs at 42C/65C.
Running at speed 3 made no difference.
Adding a third rad, boiler runs at 42C/57C.
Adding the HW circuit, boiler runs at 45C/68C.
Adding all rads (9), boiler runs at 41C/60C.
All this is shown on the following graph:
View media item 10321
I think the warmer HW return allows the boiler to run at a higher temperature, while the CH just trickles round. Eventually, CH builds up to temperature because the boiler doesn't short cycle on a warm HW return.
I think there must be a restriction in the CH circuit. I suspect a T-piece. The CH return is (from what I recall) a 15mm into 22mm T-piece. Could a mis-soldered joint like the following explain this behaviour?
View media item 10323
I renewed the pump to an RS60 (yes, I know it's overkill!)
Running at speed 2 with two rads, boiler runs at 42C/65C.
Running at speed 3 made no difference.
Adding a third rad, boiler runs at 42C/57C.
Adding the HW circuit, boiler runs at 45C/68C.
Adding all rads (9), boiler runs at 41C/60C.
All this is shown on the following graph:
View media item 10321
I think the warmer HW return allows the boiler to run at a higher temperature, while the CH just trickles round. Eventually, CH builds up to temperature because the boiler doesn't short cycle on a warm HW return.
I think there must be a restriction in the CH circuit. I suspect a T-piece. The CH return is (from what I recall) a 15mm into 22mm T-piece. Could a mis-soldered joint like the following explain this behaviour?
View media item 10323