No. If there is a fault, either or both could trip.
That is very true, but I do sometimes wonder what can be done what is compliant to provide twin 30mA RCD redundancy. (If one 30mA RCD fails, the other 30mA RCD will operate.)
No. If there is a fault, either or both could trip.
What do you mean?
should I just run 2 runs giving me 5mm. 30+ amp?
Ever heard of parallel conductors?No! That is not permitted and would not be compliant with BS7671. You can only have two runs as your proposing for Ring Final Circuits and that's using T&E internally and not SWA.
Quite so - and I can think of no reason why it should be 'non-compliant'.Two RCDs on the same circuit with no discrimination doesn't really matter electrically though, does it? It may be a pain if one is in the garage and one in the house.
Ever heard of parallel conductors?
installed by the sparkies is on a 2.5mm Spur (so 20A) So, I'd say 20A design - fused at 13A will be plenty
Ever heard of parallel conductors?
I assumed and took it that parallel conductors would not be allowed in such a situation where you have a DB at the shed end. You of course have the issue that one of the Line/Neutral conductors could come lose/become disconnected, thus reducing the current carrying capacity by half of the circuit should it be fed by a 32A or greater MCB.
installed by the sparkies is on a 2.5mm Spur (so 20A) So, I'd say 20A design - fused at 13A will be plenty
I missed that part, if the spur feeds a FCU what in turn feeds your shed/man cave, then 2.5mm² SWA will be fine taking into account length and voltage drop of course from the original DB.