Hi Guys,

I hope my questions are not too stupid.

On a 1.5mm 4 core armoured cable, the colours are brown, blue, black & grey.
Brown is live and blue is neutral, black and grey are extra for lighting? or is one used for an earth?

On a 2.5mm armoured cable there are 3 wires, brown, black and grey. Which one is neutral?
Shouldn't there be a blue wire like in the 1.5mm wire.

Is it ok to use the outer cable as the earth?

Andy
 
Sponsored Links
The 4-core cable is intended and coloured for three-phase + neutral, using the armour as an earth.

The 3-core cable is intended and coloured for three-phase without neutral, using the armour as an earth.

Guidance advises NOT using the black as a neutral, but in any event all cores should be sleeved with the appropriate colour sleeving at terminations.

The armour must be earthed, but whether it is possible to use it as the earth for the load installation depends on the type of earthing used on the system, the cable size and the cable length.

The possibilities range from:
- use 2 core supply and the armour for the earth
- use 2 core supply, and the armour *and* third core for the earth
- use 2 core supply, earth the armour at the supply end, isolate and insulate the armour at the load end and provide a local earth at the load installation
 
Hi Guys,


On a 1.5mm 4 core armoured cable, the colours are brown, blue, black & grey.
Brown is live and blue is neutral,

Oversleeve the black and use as earth


On a 2.5mm armoured cable there are 3 wires, brown, black and grey. Which one is neutral?
oversleeve the black and use as earth
oversleeve the grey and use as neutral
 
Thanks for the replys guys,

On the 1.5mm wire which is being used for garden lighting, what colour should be on the grey wire to sleeve it so that it powers another set of lights?

Andy
 
Sponsored Links
Also brown normally.
Grey and Black are both colours used as Live, but normally associated with Three phase.
The armour should still be earthed in addition to using the spare cores also
 
It is not essential that you use a core as Earth, the armour would usually be sufficient if terminated correctly.
That would leave you more cores as switch lines if thats what you need
 
Can I buy sleeving in 1metre sections, as 100metres would be a waste and what size sleeving do I need for 6mm, 2.5mm & 1.5mm wiring?

Andy
 
Can I buy sleeving in 1metre sections, as 100metres would be a waste and what size sleeving do I need for 6mm, 2.5mm & 1.5mm wiring?

Andy

Earth sleeving is generally available in small amounts from DIY sheds, although not sure about colours other than green/yellow. It's so cheap for even 100m that I can't imagine many people would be interested in purchasing less than that.
 
last time I looked a 1m strip from a shed cost as much as a 10m roll from my wholesaler.

Just to add CEF do it by the meter
 

DIYnot Local

Staff member

If you need to find a tradesperson to get your job done, please try our local search below, or if you are doing it yourself you can find suppliers local to you.

Select the supplier or trade you require, enter your location to begin your search.


Are you a trade or supplier? You can create your listing free at DIYnot Local

 
Sponsored Links
Back
Top