Some interesting and informative documents will be found if you google with the search term "diverted neutral" ( includes one which is not supposed to be in the public domain )
The complication is when the "official" Earth for the property is achieved by TN-C-S ( PME ) and there is also another low impedance route from the internal Earth wire to Ground. Most commonly this other route is a metalic water or gas supply pipe that has been bonded to the internal Earth at the Main Earthing Terminal. This is safe until there is a fault in the supply network which causes the supply Neutral to rise just a few volts above the potential on the bonded supply.
If DNOs wanted to protect again such (very rare) events, presumably that could achieved by installing an RCD upstream of the cutout (or, at least, upstream of where the installation's earthing conductor was derived from the neutral)?A lost Neutral ( metal theft at substation ) caused this damage, .... The source of the fire is the Main Earth Terminal
Some safety implications, yes, but in terms of what bernard has been talking about, I don't think you would ever get enough current flowing through saturated timber to melt cables and/or start fires.In our case, plastic water pipe but metal pipes to a big metal oil tank sat on lumps of saturated wet timber. Some interesting safety implications there under fault conditions.
I don't think you would ever get enough current flowing through saturated timber to melt cables and/or start fires.
The possibility of some things is so 'remote that it makes no practical sense not to 'exclude' them.Never exclude even the remotely possible exception.
Maybe so. But several things come to mind ...Some safety implications, yes, but in terms of what bernard has been talking about, I don't think you would ever get enough current flowing through saturated timber to melt cables and/or start fires.
As I said, there are some safety indications (but, in my opinion, not the one bernard was discussing) - and that is the most obvious of those 'some'. However, you can't have it both ways, if your saturated wooden blocks provided a low enough impedance to earth to result in bernard's melting earthing/bonding conductors and fires, then the 'shock risk' to which you refer would be minimised.Maybe so. But several things come to mind ... Firstly is the issue of having an outside tank that is live. Yes it's the same question over outside taps etc - if the "earth" becomes live and someone is stood on wet/damp ground then it's a significant shock risk.
My personal view remains that even your saturated wooden blocks are not going to result in enough current (under 'lost TN-C-S' neutral conditions) to result in a dangerous rise in the temperature of even bonding conductors, let alone copper pipes.And then there is another question as to what happens to the copper pipe. Would enough current pass to warm it up, and at what point does this become dangerous ?
My personal opinion is as above.And finally, consider that the conductive area of these lumps of timber (old railway sleepers) is substantial - considerably more than that of a thin earth rod - but insignificant compared with a metal water pipe.
If the number and quality of earth rods were such that supplies were 'more-or-less normal', I would imagine that a 'lost neutral' might go un-noticed more-or-less indefinitely..... But then there comes the discussion : if every house had an earth rod, and the neutral was sufficiently constrained so supplies were more or less normal - could the loss of a neutral go un-noticed for a while ?
Well, yes and no.You speak as if 'having to maintain a PME earth' is some sort of burden - but it surely is a total 'non-burden', since it merely means that they have to maintain the neutral connection to the property (which they obviously have to, anyway)?
Yes, it does seem to be harder than some of the documentation suggests. But, when looking for something else in the BBB I spotted in section 2 that Ze references 313.1 where there is a note that says "The above information should be provided by distributors on request (see Appendix a sec 2)". App2 sec 2 helpfully points out that Regulation 28 of the ESQCR 2002 requires distributors to provide the following information to relevant persons free of charge - with a list that includes everything I asked about.One of the questions in the 18th exam relates to 132.2 and includes getting that info by Enquiry, which obviously seems not that easy.
The pedant in me has been ruminating on that for a bit. The device isn't voltage operated, it's current operated - with fault currents going to the earth rod via the device - and the current creating a magnetic field that operates the trip mechanism. The voltage is a result of the resistance & inductance of the operating coil - but the operating characteristic is the current required to trip the mechanism rather than the voltage across it.This was the Voltage Operated Earth Leakage Breaker ( VOELB ) which compared the voltage on the Earth wire inside the property with the voltage on the ground rod.
I'm not sure that that would be so much a case of 'maintaining a PME earth being a burden' as a complete hash-up of 'agreeing that it was PME' in the first place - since it's very unlikely that the impedance of their neutral conductor would ever increase.Well, yes and no. It might be a burden if they've agreed that it is PME, and then the electrician helpfully points out that Ze is above their limit.
In the case of an L-CPC fault, a VOELCB should certainly operate if the pd between exposed-c-ps and true earth rises to a 'dangerous' level (>50V or whatever) (although no level of such a pd should really be 'dangerous' if there is a proper equipotential zone), but an RCD will result in that threshold pd being lower (even with TT and very much lower with TN).[of VOLECBs vs RCDs] .... So apart from sensing current in the earth rod connection rather than difference between line & neutral currents, both perform the same function - disconnect the supply if a fault passes enough current to cause a potentially dangerous voltage on the protective conductors.
The device isn't voltage operated, it's current operated