Wow you fitted a lot in here
This used to be quite a big issue, I did some exploratory work in a factory where the power ratings and power cost didn't tally, there were 2 similar buildings strewn with the same set of twin 8ft 125W fittings which ran 24/7, one was used as the factory with machinery and the other for storage. The metered power for both buildings was similar until the factory closed for a number of months for a refit, there was a bigger than expected reduction in power. We checked out the lighting and found the storage area was running on a much higher voltage, well over 240, and the factory was well under 230 [different sub's] and the increase in power was not linear with the increased voltage. We also concluded one phase of the factory was very near the voltage at which the lights extinguish at times and need more frequent tube changes.Since we are told we must fit two 30 mA at 40 mS RCD's in series with boats and caravans, can't really say it is wrong to fit two in series, even if a little pointless, you could always change garage one to 10 mA.
As to MCB where it is likely you can overload then having some discrimination may be prudent, my caravan has a 10A and 6A MCB which is fed from a 16A outlet which means if I put the kettle on with heater running in error I can reset without going outside. But before you go up in a rating you would need to inspect and test to see if you can without changing some thing else. I have seen many lighting circuits where the 6A has been swapped for at 10A however although the cable can take 10A, and your permitted up to 16A for a lighting circuit, the ceiling rose which acts as a junction box is only rated 6A (although sure it can handle a lot more) so technically you should not fit a 10A MCB in lighting circuits which have 6A ceiling roses.
So you would need to check on the ELI before you can change to a larger MCB.
As to volt drop and if the appendix is considered as a regulation well when one takes the C&G2382 exam they do ask questions about items in the appendix so it would seem C&G consider the appendix as part of the regulations. However in real terms looking at fluorescent lights. With the old wire wound ballast the fluorescent lamp was very sensitive to voltage, a 230 volt fitting can draw well over rated current if fed with 254 volt, and can fail to strike at 215 volt. I had a 240 volt 65W fitting in my kitchen, supply to house was around 245 volt, with a 58W tube as 65W discontinued it would strike most days, but then it stopped working all together. On testing voltage now house is at 230 volt, seems some solar panels have been fitted in the street and so they don't lock out on over voltage the voltage needs to drop.
Been caught out with this where a circuit was designed for the measured ELI figures and it was marginal, DNO did some alterations (moved cables for a road development) and the ELI went up making the circuit non compliant.This has been talked about a few times, we can test incoming supply and it may be 240 volt with an ELI of 0.20Ω but without telling you, the supplier can change that to 230 volt with an ELI of 0.35Ω as for ELI with all RCD protection not really a problem, but volt drop is another matter.
Did a disco in a church hall a good mile of pole route from the village many many years ago and supply voltage as flaky as hell, the mains hum in the speakers was significant and I really thought my kit had developed a fault and tried providing my own earth spike and isolating from halls earth, the music was even modulating the lights in the church.I have been caught out a few times with volt drop, but fluorescent fittings and transceivers the latter receives OK with volt drop, but on transmit it can have mains hum which one is unaware of. OK licensed ham should know better and CB limited to 4W and pre switch mode power supply radios, or record players you can hear the main hum as voltage drops so well aware of problem.
I think fluo fittings are running much hotter than before as they are now designed to strike at the lower voltages but generally still run >240V, so much for improved efficiency .As said other than pre-HF ballast fluorescent fittings there is very little likely to fail due to volt drop. In the main the modern SMPS has removed the problem with volt drop. However one tends to use old equipment in garages, you buy a nice new radio alarm for bedroom, and old one it taken to garage.