Moved into 4 bed detached Victorian house last year. Wasn't particularly warm over winter and have decided to investigate. Found boiler is short cycling, 2 minutes on 2 minutes off. Boiler switches off when outlet temp reaches about 75 C, and inlet temp is 55 C. Cleaned out system with Sentinel x800, but that has had no effect.
Found bypass valve was always open so took that off and found it jammed with black gunge. Put in a new one which stayed closed until I foolishly turned down pressure, now that one will not close!. Replaced it temporarily with stop ends.
Knowing boiler output and delta temp over output, calculated flow rate through primary and hot water tank circuit at 16 litres / min. Have put pressure gauge where bypass was, after pump and before motorised valves. Static pressure is 1.7m. This increases to 2.4m (0.7m above static) when pump is running and hot water tank circuit motorised valve is open. Gauge reads 3.2m (1.5m above static) when pump is running and valves are closed. Pump is BG Grundfos multihead G that I cant find curves for. Pump setting 3. Have curves for selectric and super selectric which I understand are similar and give a maximum head of 5 to 6 metres, and a head of 4.5 to 5 metres at a flowrate of 16 litres / min
So it looks as if the pump isn't producing the required flowrate and head. The piping immediately before and after the pump strongly attracts a magnet, and water drained from the pump is dirty. Could the dirt be affecting the pump? If I replace the piping could I clean the pump? I see there are cheap refurbished BG Grundfos multihead Gs available - are they any good? I'd love to hear your thoughts on how to proceed. Thanks
Found bypass valve was always open so took that off and found it jammed with black gunge. Put in a new one which stayed closed until I foolishly turned down pressure, now that one will not close!. Replaced it temporarily with stop ends.
Knowing boiler output and delta temp over output, calculated flow rate through primary and hot water tank circuit at 16 litres / min. Have put pressure gauge where bypass was, after pump and before motorised valves. Static pressure is 1.7m. This increases to 2.4m (0.7m above static) when pump is running and hot water tank circuit motorised valve is open. Gauge reads 3.2m (1.5m above static) when pump is running and valves are closed. Pump is BG Grundfos multihead G that I cant find curves for. Pump setting 3. Have curves for selectric and super selectric which I understand are similar and give a maximum head of 5 to 6 metres, and a head of 4.5 to 5 metres at a flowrate of 16 litres / min
So it looks as if the pump isn't producing the required flowrate and head. The piping immediately before and after the pump strongly attracts a magnet, and water drained from the pump is dirty. Could the dirt be affecting the pump? If I replace the piping could I clean the pump? I see there are cheap refurbished BG Grundfos multihead Gs available - are they any good? I'd love to hear your thoughts on how to proceed. Thanks