Tacanova is directly after the pump and bridges the 30 cm or so between flow and return.
How did he work that out? And did he take into account the reduction in output due to lower working temperatures?He did say that the total radiator output is 22.8 kW
That implies that the rads are more than enough to heat the house.House is sweltering to be honest
Assuming that excludes any allowance for hot water, the rads are slightly undersized.As a rough guide (will need to measure to be precise with the width and length of the home etc) it says the requirement is 19.7kw
You said the Setter is set to 2, which is 2 litres/min. 1m³/hr is 16.67 litres/min; so 12% of the heat is being sent straight back to the boiler. This not only reduces the heat available to the rads but, more importantly, raises the return temperature unnecessarily.The tacanova setter is in 22mm
Didn't see this until I had posted my last comment.He has now advised replacing the taconova with an ABV as after reading the boiler manual he says it specifies an automatic bypass not a fixed bypass. Do you agree with that?