no. It sounds like it is jammed. You should be able to turn the spindle with your fingers. Does it need pliers?
Sorry John, what spindle exactly?
no. It sounds like it is jammed. You should be able to turn the spindle with your fingers. Does it need pliers?
..it seems as though the boiler is reaching the max temp in similar times at the start so shuts down? Then takes similar times to cool down enough to fire back up?
I timed the boiler and below is the times of on and off;
On - 2m52s
Off - 2m12s
On - 1m22s
Off - 2m12s
On - 1m02s
Off - 2m12s
On - 50s
Off - 2m30
On - 40s
Off - 2m39s
On - 39s
Assuming all you controls/valves are functioning correctly then the switching on and off of the boiler sounds perfectly ok to me. I have a Suprima as well so am familiar with normal operation. Boiler fires and heats the water - boiler stat cuts off at the set point. As the heated water circulates it gives up heat through the rads and returns cooler to the boiler. Boiler fires again to heat the cooled water, boiler stat cuts off again and so the cycle is repeated. Depending on the demand for heat (or hot water) the boiler will continue to cycle in this way until the cylinder/ room stats cease demand.
The boiler is designed as low water content so I would expect fairly short cycles of heating as there is only a small heat exchanger capacity.
Remember too that the Suprima needs a bypass circuit as it has an overrun facility to remove excess heat from the boiler AFTER all demand has ceased.
Don't confuse the operation of this boiler with that of a more modern modulating boiler as the two are considerably different.
You actually worked it out yourself in your first post.
..it seems as though the boiler is reaching the max temp in similar times at the start so shuts down? Then takes similar times to cool down enough to fire back up?
The boiler thermostat switches the burner on and off to keep the hot water leaving the boiler at the set temperature (plus or minus a degree or two)
As the radiators, pipework, rooms etc., warm up, the 'on' time gets less and the 'off' time increases. Exactly what your figures show.
I timed the boiler and below is the times of on and off;
On - 2m52s
Off - 2m12s
On - 1m22s
Off - 2m12s
On - 1m02s
Off - 2m12s
On - 50s
Off - 2m30
On - 40s
Off - 2m39s
On - 39s
Sounds like you may have a problem with the external controls though if the house is getting to 25 degrees when the room thermostat is only set at 20 degrees. Unless you have massively oversized radiators that release a lot of heat after the system goes off, or another heat source somewhere.
The bypass circuit will be a pipe from the flow to the return after the pump but before the 3-port valve. It will have some sort of valve in the pipe, might be a manual gate valve or similar, but it should not be fully closed otherwise the overrun will not work correctly. Conversely if it is set too far open it will short-circuit the flow to the cylinder and rads and they will not get fully hot.
If you need to find a tradesperson to get your job done, please try our local search below, or if you are doing it yourself you can find suppliers local to you.
Select the supplier or trade you require, enter your location to begin your search.
Are you a trade or supplier? You can create your listing free at DIYnot Local