I have just replaced my old oil fired boiler with a Ravenheat (screwfix) condensing gas fired one, and replumbed the system for fully pumped, vented, using the existing 11 radiators. The problem appears to be not enough flow through the boiler. After the sytem has warmed up, but before reaching room temp., the boiler flow pipe temp. rises to thermostat cutoff. It then falls to the switch-on point after about 1 minute, and relights the burner for 1 minute before cutting off again. It does this continuously until the room stat is finally satisfied.
If the pump speed is increased to position 3, it pushes hot water UP the vent and cold feed and into the loft expansion tank.(??)
I don't think there is any air in the system
and there shouldn't be a blockage as I've flushed out the system several times now.
Anyone got any ideas PLEASE????.