Hi, I have a Vaillant ecoTEC plus 424 ( 24KW ) boiler feeding three circuits. Down stairs heating, upstairs heating and hot water via thermostats and motorized valves. There are twelve rads and two towel rails. All rads have TRVs except the one in the entrance hall. Both towel rails on lock-shields.
Target heating flow temperature 62
Partial load set at 18KW
Anti cycle time set at 25 minutes.
Room stats set at 21.
TVRs set between 3 and 4 ( Drayton TRV4s ).
Boiler fires up ok and gradually ramps up to target flow temperature and modulates for a while until the room TRVs start closing. Stats still calling for heat so motorized valves open. Boiler quickly goes into overheat and into anti cycle. Anti cycle times out at around 6 minutes, boiler fires up and back into overheat and the cycle begins again.
Is it just a Vaillant thing ?. what do other boilers do when most or all TRVs close ?. It seems to be in a continuous circle of "over" heating just the pipework ?.
Target heating flow temperature 62
Partial load set at 18KW
Anti cycle time set at 25 minutes.
Room stats set at 21.
TVRs set between 3 and 4 ( Drayton TRV4s ).
Boiler fires up ok and gradually ramps up to target flow temperature and modulates for a while until the room TRVs start closing. Stats still calling for heat so motorized valves open. Boiler quickly goes into overheat and into anti cycle. Anti cycle times out at around 6 minutes, boiler fires up and back into overheat and the cycle begins again.
Is it just a Vaillant thing ?. what do other boilers do when most or all TRVs close ?. It seems to be in a continuous circle of "over" heating just the pipework ?.