Not quite. The output of a radiator is that which it produces under conditions laid down in British Standard BS EN 442. This specifies the temperature of the water as it enters and leaves the rad and the temperature of the test room. All of these will affect the output of a radiator. The test conditions are: flow=75C, return = 65C, room = 20C. You could produce higher output by increasing the water temperature or reduce the output by lowering the water temperature.Would I be correct in saying the btu/h watt output quoted by the manufacturer of any radiator is the maximum amount of heat output?
With modern condensing boilers, the trend nowadays is to run heating systems at lower temperatures as it means the boilers are more efficient. This can be compensated for by oversizing radiators. However, as the system is only required to produce the maximum output of a few(?) days each year, many installers would not bother oversizing the rads for the lower water temperature.
All of these factors have to be taken into account when calculating the heat loss of a room.If the height, width, length of a room, plus the amount of outside walls, the roofing insulation, the size of window, whether it had double glazing or cavity wall insulation, whether the room was a bedroom or lounge, the age of property etc etc would be taken into consideration of working out the correct heat loss programme?
Not completelyIf the heat loss worked out was 6,500 btu what would the amount of btu heat output required to heat the room be? 6,500-8,500 the minimum being the heat loss. What is the range between heat loss and heat output or heat input?
Does this make sense?
The heat loss of a room is calculated assuming certain external and internal temperatures, usually -1°C and 21°C. If you want to allow for colder weather or a warmer house, you have to make the necessary adjustment to the heat loss; fortunately it's directly related to the difference between internal and external temperatures.
Having said that, it is standard practice to allow an extra 10-20% in the size of radiators and boilers to provide for faster warming up. This is useful if the house is unoccupied most of the day. This is in addition to any oversizing for low boiler temperatures.