I've done the calculations for my house and come up with 7.1kW of heating load, 13.4kW of radiator surface. So far so good. I now have a choice of a 12/15kW or a 15/20kW boiler (HRM wallstar).
The current coal fire is rated at 11kW to water and 1.8kW to room. The later is free standing and mine's not so say about 12kW. But my feelings are that last winter the coal system struggled. I guess it could be that the fire is not producing 11kW to the water as it was probably rated on Welsh anthracite, not the imported stuff we get these days. Or my calculations could be off but I've checked these (it's only plugging numbers in a program after all).
So, the 12/15 would seem to be the one to choose but on the other hand the 15/20 would give more in hand, for say a future conservatory. Also, the 12/15 is only just bigger the current coal fire so it feels too small. The 15/20 matches the kitchen cupboards better perhaps as it is 700mm high like they are. The 12/15 is only 600mm high.
Are there any disadvantages to choosing the 15/20? With so much radiator I can't see it cycling significantly more that the 12/15 as the cycle would be mainly the room stat I would think, yes?
The current coal fire is rated at 11kW to water and 1.8kW to room. The later is free standing and mine's not so say about 12kW. But my feelings are that last winter the coal system struggled. I guess it could be that the fire is not producing 11kW to the water as it was probably rated on Welsh anthracite, not the imported stuff we get these days. Or my calculations could be off but I've checked these (it's only plugging numbers in a program after all).
So, the 12/15 would seem to be the one to choose but on the other hand the 15/20 would give more in hand, for say a future conservatory. Also, the 12/15 is only just bigger the current coal fire so it feels too small. The 15/20 matches the kitchen cupboards better perhaps as it is 700mm high like they are. The 12/15 is only 600mm high.
Are there any disadvantages to choosing the 15/20? With so much radiator I can't see it cycling significantly more that the 12/15 as the cycle would be mainly the room stat I would think, yes?