We still dont know if the OP has a second pump and blending valve.
If it does then the temp setting is required on the blending valve. Although if the boiler temp is lower that will still work.
40-45 C is usually the highest temp to supply to UFH. What is required depends on the floor construction and the level of insulation in the building. Better to start at 35 C and see how that works.
A USB temp monitoring/recording sensor is ideal for setting up a UFH system.
In an ideal world the temp would be supplied at the max initially to obtain the fastest heat up and then reduced as the house approaches the set temp. But thats in the realms of an intelligent adaptive controller.
Tony
If it does then the temp setting is required on the blending valve. Although if the boiler temp is lower that will still work.
40-45 C is usually the highest temp to supply to UFH. What is required depends on the floor construction and the level of insulation in the building. Better to start at 35 C and see how that works.
A USB temp monitoring/recording sensor is ideal for setting up a UFH system.
In an ideal world the temp would be supplied at the max initially to obtain the fastest heat up and then reduced as the house approaches the set temp. But thats in the realms of an intelligent adaptive controller.
Tony