We still dont know if the OP has a second pump and blending valve.

If it does then the temp setting is required on the blending valve. Although if the boiler temp is lower that will still work.

40-45 C is usually the highest temp to supply to UFH. What is required depends on the floor construction and the level of insulation in the building. Better to start at 35 C and see how that works.

A USB temp monitoring/recording sensor is ideal for setting up a UFH system.

In an ideal world the temp would be supplied at the max initially to obtain the fastest heat up and then reduced as the house approaches the set temp. But thats in the realms of an intelligent adaptive controller.

Tony
 
Sponsored Links
It's got the pump on the boiler to send it up to the manifold &the pump to send the water round the UFH pipes. I'm not too sure what u mean by a blending valve? So I presume it hasn't got one :mrgreen:
I contacted glow worm & they understood what I was asking but didn't have an answer.
So I'll just try it between 35-40 to start off with but when winter comes round raise it a little.
I,ve only just built the house so I went crazy with the kingspan so it's probably a bit over rather than under insulated.
 
By the second pump there would usually be a blending valve!

Something with three pipes one to the second pump, one to the return and one to the flow. This would have a temperature adjustment and often a scale to assist with setting!

With no rads the blending valve and second pump are not really required. They are not used in most of Europe but installers here dont usually seem to realise that.

Tony
 
By the second pump there would usually be a blending valve!

Something with three pipes one to the second pump, one to the return and one to the flow. This would have a temperature adjustment and often a scale to assist with setting!

With no rads the blending valve and second pump are not really required. They are not used in most of Europe but installers here dont usually seem to realise that.

Tony
 
Sponsored Links
cookie11 wrote
unless you mean the thermostatic control valve that has a brass probe inserted just before the manifold

Does it have this device you outlined earlier? And does it have a name printed on the components anywhere?
 
dont think it has anything like that,
its a hep2o system with a giacomini manifold & actuators.
all it as is like i said before the flow reaches the manifold it has a thermostatically controlled valve which has a brass probe on the manifold, this is to stop too hot water from entering the manifold i presume.
other than that its just a manifold with a pump on it.
 
mixing-manifolds1.jpg
 
Slightly unusual but it will work as long as there is an auto bypass valve.

Tony
 
yep it works great, had it running brilliantly on 3 levels of the house but just wanted help fine tuning it.
& the big white knob on the top right is the bypass valve.
 