Wondered if anybody has any ldeas that may help solving our heating problem.
When we got back from a month away last week the radiators downstairs were all cold but upstairs was very hot. We had left our thermostate which is downstairs in the hall set on 15 degrees and the timer on constant to keep the house aired out. Our plumber first thought it was a blockage as he tested the pump and it was still spinning although rather noisy. He bought something to flush the system but this made it worse and the boiler cut out so he said he would drain and flush the system the next day.
After draining and flushing it was the same so he thought the pump should be replaced as it was 18 years old and noisy. I purchased a new Grundfos Alpha plus pump whiich was fitted yesterday but still no improvement and the boiler cuts out after five minutes and nothing even starts to heat up!
Also the header tank in the loft was full of brown sludge that was also weighing down the ballcock which has been cleaned now but I am wondering what caused it and if some has got into the pipework. We did put a hose in the header tank & back flush it and it appeared to drain ok.
He says that the radiators all filled and there is no air in them so either there is air trapped in the boiler or the thermostats on the boiler have failed. I am not convinced this is the problem and any suggestions would be welcome please!
When we got back from a month away last week the radiators downstairs were all cold but upstairs was very hot. We had left our thermostate which is downstairs in the hall set on 15 degrees and the timer on constant to keep the house aired out. Our plumber first thought it was a blockage as he tested the pump and it was still spinning although rather noisy. He bought something to flush the system but this made it worse and the boiler cut out so he said he would drain and flush the system the next day.
After draining and flushing it was the same so he thought the pump should be replaced as it was 18 years old and noisy. I purchased a new Grundfos Alpha plus pump whiich was fitted yesterday but still no improvement and the boiler cuts out after five minutes and nothing even starts to heat up!
Also the header tank in the loft was full of brown sludge that was also weighing down the ballcock which has been cleaned now but I am wondering what caused it and if some has got into the pipework. We did put a hose in the header tank & back flush it and it appeared to drain ok.
He says that the radiators all filled and there is no air in them so either there is air trapped in the boiler or the thermostats on the boiler have failed. I am not convinced this is the problem and any suggestions would be welcome please!