As I said, your aswer (to Simon's question, if that's what you're talking about) corresponds with what I have always suspected - so I guess you must be rightOH Im pretty sure mine was the most accurate answer
I wouldn't have expected many votes because I presume that very few people have actually seen/read the Standard and so, like me, have no sensibly-based 'beliefs' about what it 'requires'.Not many votes yet, I'll leave it till the poll closes before I hand out the answers. Meanwhile, anyone have any comments/discussion point on the standards rather than the wording of the poll ?
I realise that and, as I have said (and as I suspect might also be your view), I strongly suspect that those who say "a CU must have <some attribute>" are all, or nearly all, wrong - but, not having had an opportunity to read the Standard, I just don't know what to believe - so any vote I cast would be a sheer guess.The poll wasn't so much about what the standard does say, but about what people think it says. I'm just going by the number of threads where someone has said something along the lines of "a CU must have <some attribute>".
Not many votes yet, I'll leave it till the poll closes before I hand out the answers. Meanwhile, anyone have any comments/discussion point on the standards rather than the wording of the poll ?
We know that, but you said that you would tell us 'the answers' when it closed - but it sounds as if you are a bit too busy at present. We will therefore wait with bated breath!Yeah, polls have a defined time to remain open.
Had you worded the question literally like that, I would probably have been equally (if not more) disinclined to vote - since it would then have been a bit ambiguous ... whilst, like you, I know what "a lot of people think it says", I suspect that they are probably all wrongThe poll wasn't so much about what the standard does say, but about what people think it says.
Indeed, but the rest of that sentence reads ..BS7671 says :
536.4.201 Fault current (short-circuit) ratings
... For an installation with a 230 V single-phase supply rated up to 100 A that is under the control of ordinary persons, switchgear and controlgear assemblies shall either comply with BS EN 61439-3 having a suitable fault current (short-circuit) rating for the maximum prospective fault current at the point of connection to the system or be a consumer unit ...
... which seems to be a bit more specific.536.4.201 of BS7671] ... [a consumer unit] incorporating components and protective devices specified by the manufacturer complying with
BS EN 61439-3, including the 16kA conditional short-circuit test described in Annex ZB of the standard.
As you will realise, that essentially corresponds to what I had always suspected - in short, nearly all the things that some people think/believe it says are actually myths.So in summary :
100A - not a hard requirement
Single phase - ditto
- these two, if complied with merely simplify a couple of bits of 7671
16kA breaking capacity - only required if you don't calculate/measure the prospective fault current. But not exactly hard to comply with anyway
Will contain a fire - can't find any requirement
Self closing door - no
Indeed. As stillp always used to remind us, it is theoretically possibly to access most (all?) British (and maybe other) Standards at a public library - but I have to say that, even without Covid-19, I always have had better things to do with my time that to commute to/from such a place (well over an hour round trip for me)!Thank you Simon, it has been a problem since I started as an electrician, that near impossible without spending a lot of money on the books to find out myths from fact, which is not helped by trade articles which are clearly designed to sell their goods not give facts.
That's what I would have thought.You should not need a journey because many libraries are signed up to the British Standards On Line service. So you log into the portal through your library website.