Call out to no power to sockets. Found 3036 fuse blown (and by the looks of it, had done several times!).

Voltage operated ELCB in place on a TT system, 5.8ohm Zdb.

Rodent damage in loft, causing earth fault.

The earth fault on the cable would cause around 40amps to flow, damaging the 2.5mm T+E - every so often an L to N fault blowing the fuse with a bang.

Have replaced damaged cable, checked insulation resistance, and have fitted an RCD temporarily while quoting to replace fuseboards initially with a view to a rewire.

Quite shocking - a real fire risk.

1313521924.jpg


1313521928.jpg


1313521930.jpg


1313521931.jpg


1313521933.jpg


1313521935.jpg


1313521937.jpg


1313521942.jpg
 
Sponsored Links
Voltage operated ELCB in place on a TT system, 5.8ohm Zdb. Rodent damage in loft, causing earth fault.
Sounds like one of those cases in which the main bonding has prevented the ELCB from operating in response to the earth fault?

Kind Regards,John.
 
Sponsored Links
Exactly why the ELCB's are to be condemned when seen.
Quite so - although, to be fair, I suppose they do what it says on the tin, and what they were presumably designed to do - namely operate if the potential of CPCs rise to 50V (or whatever) above earth potential. However, since such a rise in potential is not really that much of an issue if adequate 'main bonding' is in place, I wonder if such bonding was less in evidence in the days when VO ELCBs were introduced?

Kind Regards, John.
 

DIYnot Local

Staff member

If you need to find a tradesperson to get your job done, please try our local search below, or if you are doing it yourself you can find suppliers local to you.

Select the supplier or trade you require, enter your location to begin your search.


Are you a trade or supplier? You can create your listing free at DIYnot Local

 
Back
Top