Although Haisham suggests an auotadapt can be set up with auto bypass, doing so will inevitaby push the boiler needlessly out of condensinng state more than neccessary,
It's not inevitable. If the bypass is correctly set up, it will only open when conditions demand it. I have demonstrated, in an earlier post, that your system can be run at low temperatures, even in the coldest weather.
where does grundfos have instructions on how to set the bypass press on an auto bypass with an Alpha autopump?
http://net.grundfos.com/Appl/WebCAP...FAM&appcode=HEATING&pdfid=776425&language=ENU
The problem is that that you need to know the minimum flow rate through the boiler and many manufacturers do not supply that info or, if they do, the info is inaccurate (e.g Vaillant).
Grundfos say that ABVs are not compatible with Autoadapt and recommend using PP2, the highest proportional pressure setting instead.
Have you considered that your pump may not be large enough for your installation?
At max output of 30kW with a 20°C differential the flow rate is 1220 litre/hr and the pressure loss through the boiler is 2.4m (see installation manual). At that flow rate the pump can deliver a maximum head of approx 3.4m so the head available for the loss round the system is approx 1m. You said earlier that you have 24kW of rads but not how many; I would guess at between 15 and 20. In that case the system loss is likely to be more than 1m.
You can work it out using the info given in
Small Bore heating Systems and
Copper Tubes in Domestic Heating Systems