Hi Smokebox and all
well I've just sat and read through this entire thread properly and the Vaillant manual and have noticed that one of the problems is that you don't know the boilers min flow rate
The minimum flow rate of your boiler is 20.3 L/min, it's in the specification table on page 8 of your manual
also
3.14 Pump specification
A variable duty pump should be set to give a
temperature difference of no greater than 20°C
so now you have
your min flow rate
recomendations regarding variable pumps
tech info on your pump regarding flow rates and recomendations reg auto bypasses
and a couple of diagrams regarding using valves/solenoids etc for overrun bypassing
you should have enough info now surely
Matt
well I've just sat and read through this entire thread properly and the Vaillant manual and have noticed that one of the problems is that you don't know the boilers min flow rate
Only Vaillant can advise a satisfactory MINIMAL ACCEPTABLE FLOW IN LITRES PER MINUTE. for thispurpose....... only they don't understand or refuse to specify, and eventually get rather rude to emails until you write to the UK Managing director. but they still don't know. One technician said the boiler flow must never fall below 1220 l/hr - a real jester! and I suppose he is paid!
The minimum flow rate of your boiler is 20.3 L/min, it's in the specification table on page 8 of your manual
also
3.14 Pump specification
A variable duty pump should be set to give a
temperature difference of no greater than 20°C
so now you have
your min flow rate
recomendations regarding variable pumps
tech info on your pump regarding flow rates and recomendations reg auto bypasses
and a couple of diagrams regarding using valves/solenoids etc for overrun bypassing
you should have enough info now surely
Matt