If you spur from a ring in the house to the garage and then installed a small CU in the garage, any problems in the garage can still trip the RCD in the house CU. You'd lose some or all of the electrics in the house as well as the garage so that's very inconvenient and certainly doesn't provide 'garage protection self contained within the garage'.

The 13A fuse on the ring can blow for sure, but unlikely as lower trip values are inside the garage. As the garage piggybacks the ring if the ring drops out so does the garage of course, which is far from ideal.

I didn't mean that the FCU on the ring would blow, I'm saying the house RCD will trip and you'll lose all power to the house and garage. A faulty appliance in the garage or water ingress or earth leakage etc will trip the house RCD which will be very irritating to family members. Also if you have a high load in the garage (but not so high as to trip the garage MCB) and people in the house are using the ring then that would make the MCB on the ring trip.
 
Sponsored Links
An mcb's prime function is to check current overload. The 16A mcb will trip before the 20A. But this was to make a poor job better, but not the ideal (which is the garage cable back to the CU). The setup was far better than what was before, for sure.
 
Last edited:
I didn't mean that the FCU on the ring would blow, I'm saying the house RCD will trip and you'll lose all power to the house and garage. A faulty appliance in the garage or water ingress or earth leakage etc will trip the house RCD
Of course it will. That is the case with all installations with one or two RCDs. The only way to ensure all faults or overloads are contained in the garage is not have the ring on an RCD or rcbo, having the garage circuits on RCBOs/RCD. But the house is then less protected, which is undesirable.
 
Last edited:
Sponsored Links
The only way to ensure all faults or overloads are contained in the garage is not have the ring on an RCD or rcbo, having the garage circuits on RCBOs/RCD.

There are lots of other options, such as not spurring from the ring (but I appreciate that's probably beyond the changes you are looking to make at the moment).

An mcb's prime function is to check current overload. The 16A mcb will trip before the 20A.

If you are drawing 15A in the garage and 15A on the ring then the ring MCB will trip before the garage. It depends how the ring is being used whilst you are working in the garage. The garage MCB won't always trip first just because it's rated lower.
 
If you are drawing 15A in the garage and 15A on the ring then the ring MCB will trip before the garage. It depends how the ring is being used whilst you are working in the garage. The garage MCB won't always trip first just because it's rated lower.
Of course - obvious. Draw 15A in the garage and 16A on the rest of the radial then the 20A in the main CU will trip.
 
There are lots of other options, such as not spurring from the ring (but I appreciate that's probably beyond the changes you are looking to make at the moment).
I did actually split a ring into two radials with an explanation on how it was done.
There is also a hypothetical garage spur off a ring, and the ideal way of doing it - this has created much confusion. But thanks to Sunray, again, that was sorted,
 
Oh boy. Last night I actually thought 'All we need now is for Winston to join in and introduce even more carp into the thread', lo and behold I find Winston has joined in and introduced his load of...

Hang on Winston has added some very good comments, well done, and it's nice to be able to say that.
An mcb's prime function is to check current overload. The 16A mcb will trip before the 20A. But this was to make a poor job better, but not the ideal (which is the garage cable back to the CU). The setup was far better than what was before, for sure.
It's debatable, I do a fair amount of temporary work and it's quite common to have several closely related MCBs in line. In the event of a short circuit fault I've had a 10, 16, 20 & 32A all blow, equally on an overload I've known a B25 trip at the load before the C16 at the source, from the curves it shouldn't have happened that way.

A sub CU fed by a FCU is a common set-up. I had new house like this about 18 years ago. A whole estate was like that. I told the builders to run a full armoured cable back to an mcb in the CU. They said "no, it was legal and safe". I checked and it was within regs, etc. I didn't like it as the garage CU's main fuse was 16A with FCU's the fuse 13A. Clever eh. The 16A fuse was useless. If something was wrong in the garage i did not want to change a fuse in the dining room, wanting all garage protection contained within the garage.
In which case it should have been reported to their scheme provider as it is a useless set-up, albeit not dangerous.

However having seen the rest of the replies since my last post I'm totally convinced HW is only here for a wind-up, either that or a stupid botcher, although that is an insult to the trade of botching.
 
Oh boy. Last night I actually thought 'All we need now is for Winston to join in and introduce even more carp into the thread', lo and behold I find Winston has joined in and introduced his load of...

Hang on Winston has added some very good comments, well done, and it's nice to be able to say that.
It's debatable, I do a fair amount of temporary work and it's quite common to have several closely related MCBs in line. In the event of a short circuit fault I've had a 10, 16, 20 & 32A all blow, equally on an overload I've known a B25 trip at the load before the C16 at the source, from the curves it shouldn't have happened that way.
All you can do is put in the correct mcb type values. If they trip out of order than t may be the mcb which is at fault.
In which case it should have been reported to their scheme provider as it is a useless set-up, albeit not dangerous.
I did complain to the builder (Taylor Woodrow) who did not want to know. They said it conforms to regs and is totally safe. I pointed out that the garage fuse is 16A which is useless as the FSU is 13A. Nothing from them. The only way to get them to put it right was a dodgy way via lawyers. If I lose I pay a big lawyers bill. I thought it is best I improve it myself.
However having seen the rest of the replies since my last post I'm totally convinced HW is only here for a wind-up, either that or a stupid botcher, although that is an insult to the trade of botching.
I am doing is just answering the posts - no more. Some responses are odd for sure. Please show me where I have botched anything - one of your professionals was advocating a 4mm spur cable off a 2.5mm ring with socket and FCU off it. Read it, it is there, I never made it up. Look at some of the replies - these are professionals? My oh my! :eek:
 
Last edited:
Should say try to wind us up. You post nonsense and you refuse to give any details as to what you are trying to do. I really am not wound up.
Another one. <sigh> His value to the thread topic has been zero. More noise.
 
Last edited:

DIYnot Local

Staff member

If you need to find a tradesperson to get your job done, please try our local search below, or if you are doing it yourself you can find suppliers local to you.

Select the supplier or trade you require, enter your location to begin your search.


Are you a trade or supplier? You can create your listing free at DIYnot Local

 
Status
Not open for further replies.
Sponsored Links
Back
Top