For a start, assuming you are using T+E cable (not singles) you should be using either 4D2A or, better (since it's slightly kinder!) 4D5!I've now got;
It - 32/(1*1*0.78*1) It - 41A So It > In - All Good?
But then using table 4D1A And Reference Method B - It has to be 6/10mm cable - Obviously not right.
Yes. You're really doing this back-to-front. The requirement (per 433.1.204) that for a ring final protected by an MCB with an In of 32A, the CCC of the cable should be at least 20A. By my reckoning, if it's Method B and you have a de-rating factor of 0.78, then 4mm ² cable would be fine (and 2.5mm² "would not be far off" - not that that is much consolation!). That 'dispensation' applies only to ring finals. For any other (radial) circuit, the CCC of cable in a circuit protected by a 32A MCB has to be at least 32A, not 20A.Is there a rule for sizing cables in a RFC? Two legs, reduction in CSA for instance? (I'm really not sure and struggling with this!)
KInd Regards, John