Thanks. You last point is the only one I don't follow. I think I will need to draw it out, and maybe that will make it clear. Or if not maybe you'd comment on my drawing. For the moment I can't see how E and N form a parallel circuit - within my installation N is completely separate from E. The two would join at my end of the supply cable (assuming TNCS). The supply PEN in turn only connects to true earth at one point, at the supply transformer. How does any of my neutral current make it's way off the PEN to seek an alternative route?That is true, but it is also true with a single-customer TN-C-S supply. The path to earth back to the transformer via bonded items is in parallel with the 'proper' route via the supply N/E conductor - the return current to the transformer will therefore be shared between the two paths. If, as can happen, bonded water supply pipes provide a very low impedance path, a substantial proportion of the total 'neutral' current can flow via that route - hence the requirement for larger bonding conductors with TN-C-S installations.It also seems to be suggested that on a multi customer PME supply there could be significant currents carried by bonded items even in normal operation.
Tony S