May I ask where what states this?...however it states that the tester must be able to rectify the faults found...
May I ask where what states this?...however it states that the tester must be able to rectify the faults found...
Nothing wrong with that either - as long as it is only one socket, even a double.
I took it up with the company that did the eicr and they said
“I have been told by an electrician that 50a is fine for a 9.5 kw shower – Yes he is right that a 9.5KW shower will not overload the cable put 6mm cable can’t carry 50 amps so there’s a potential to overload the cable if a bigger shower was to be installed in the future, this is definitely a code C2 all day long and most inspectors would agree, as well MCB’s are not expensive. 50 amp MCB should never have been installed in the first place for a 6mm cable so this would be poor workmanship (this is also in the best practice guide as a C2).”
Hi, Im a residential landlord and have a couple of mcbs that have been flagged up on the eicr to change the rating of , I know what to do but have no qualifications apart from pat testing.
Can I change them myself or do I need to get someone in to do it ?
Also one of them is a 32a one on an electric shower, presumably they want it to be 40a however it never trips, is that really necessary ?
thank you
I am sure you can see the flaw in their explanation.I took it up with the company that did the eicr and they said
“I have been told by an electrician that 50a is fine for a 9.5 kw shower – Yes he is right that a 9.5KW shower will not overload the cable put 6mm cable can’t carry 50 amps so there’s a potential to overload the cable if a bigger shower was to be installed in the future, this is definitely a code C2 all day long and most inspectors would agree, as well MCB’s are not expensive. 50 amp MCB should never have been installed in the first place for a 6mm cable so this would be poor workmanship (this is also in the best practice guide as a C2).”
Maybe I have got it wrong, I have looked and now can't find it. However as far as doing the EICR myself it does state:-May I ask where what states this?
so if you can't do the remedial work, then your not qualified.“qualified person” means a person competent to undertake the inspection and testing required under regulation 3(1) and any further investigative or remedial work in accordance with the electrical safety standards;
so it seems if for example there is a fault on the immersion heater, but there is central heating so not really required, one can't simply isolate it?to ensure that every electrical installation in the house is in proper working order and safe for continued use;
Where is this new guidance for landlords? I can find many web pages which say what they think should the qualifications should be, but not a government one.The Electrical Safety Standards No 321 said:Carrying out an inspection of electrical installations is a complex task that requires an extra level of qualification and competence achieved beyond the standard 4-year vocational route commonly followed by qualified inspectors and testers. Therefore, Government will develop, with industry experts, new guidance for landlords stipulating who can carry out the mandatory electrical installation checks.
They don't write the regulations.that’s a bit of a presumption, they no nothing about our experienceand the best practice guide is a recognised document by the NICEIC, ECA, EAL, British Gas, Beama, AESM, BSI, Certsure, City & Guilds, IET, Napit, Spaces & Select so I’m not sure how this means we are not knowledgeable enough when all these companies support the document.
That is irrelevant.The bottom line is that this is poor design and there’s nothing stopping someone in the future installing a bigger rated shower which could overload the cable.
It doesn't have to. See 433.3.1The circuit does not comply with Regulation 433.1.1:
The conductor does not require protection against overload.The operating characteristics of a device protecting a conductor against overload shall satisfy the following conditions:
(i) The rated current or current setting of the protective device (In) is not less than the design current (Ib) of the circuit, and
(ii) the rated current or current setting of the protective device (In) does not exceed the lowest of the current-carrying capacities (Iz) of any of the conductors of the circuit
Only if the circuit requires overload protection. Your shower circuit does not.Its like saying lets just install 32amp MCB’s or bigger MCB’s than cables can carry on all circuits, we know that the circuits will use less amps than the cable can carry, they are talking utter non-sense.
Well, then they are wrong as well.I spoke to the NICEIC technical helpline and they agreed.
It would not surprise me if a lot of inspectors would, indeed, 'agree' (i.e. act/code the same), but that doesn't necessarily make it correct.I took it up with the company that did the eicr and they said
“I have been told by an electrician that 50a is fine for a 9.5 kw shower – Yes he is right that a 9.5KW shower will not overload the cable put 6mm cable can’t carry 50 amps so there’s a potential to overload the cable if a bigger shower was to be installed in the future, this is definitely a code C2 all day long and most inspectors would agree, as well MCB’s are not expensive. ....