- Joined
- 27 Nov 2024
- Messages
- 9
- Reaction score
- 2
- Country
Interestingly too even if I turn off the pump now. The boiler will still whir as if its going to fire up.
Well, as others have said, probably a job for a decent heating engineer (sounds like you’re struggling to find one though). If you could find the voltage then that’s half the battle.Interestingly too even if I turn off the pump now. The boiler will still whir as if its going to fire up.
As I said in #5If boiler AND pump running on the it's a MCV issue as microswitch is remaining depressed.
No problem. See #5Apologies yes. It would be an s plan then
Hey, it was me he was apologising to!No need for apologies
I have had someone look at the MCVs and one was replaced as was stuck.No problem. See #5
The valve stuck, or the microswitch?I have had someone look at the MCVs and one was replaced as was stuck.
The microswitch closes when the valve opens, but can stick closed.The others appear to be operating, I can them open when I call for demand on the correlating area.
As I said in #5
Yes I know, but it was stated in the very first post that’s there’s dual zones, so maybe you owe the apology?Hey, it was me he was apologising to!
But he didn't say what valves and control system he has. That's why I was asking. Who should I be apologising to?Yes I know, but it was stated in the very first post that’s there’s dual zones, so maybe you owe the apology?
But he didn't say what valves and control system he has
It runs on a 2 zone system for heating, thermostat in living room for downstairs and hallway for upstairs. With a seperate water programmer under the boiler.
The OP, since he apologised to you even though he hadn't done anything wrongThat's why I was asking. Who should I be apologising to?
I don't see the logic of that. I hadn't accused him of anything, or wanted, or expected an apology. In any case, my #24 was only a bit of fun, hence theThe OP, since he apologised to you even though he hadn't done anything wrong
Normally the pump would be connected to the boiler in order to provide pump over run.
If boiler is in cold area they sometimes run pump if boiler is at less that 5 C as a frost protection precaution!
Also pump was running during summer. OP selected null speed setting to disable the pump. Boiler would still be firing but heat from it going nowhere as pump not spinning now.Boiler also firing Tony.