Let's start again and be pragmatic and pedantic.
However, this goes against the regulations governing ring final circuits, good workmanship and proper design.
Only accessories, not appliances, should be connected on a ring.
It would (only) be unsafe with regard to the loading of the ring - both balance and total.
The spur itself would be fine.
It is just wrong.
If by 16A spur, you mean connect a 16A oven to a spur from a ring final circuit, then it could be considered a 27A spur as that is the current carrying capacity of 2.5mm² cable and it would not necessarily require fusing down because the oven will not draw more than its 16A load.am a bit puzzled why you can't take a 16A spur from a 32A ring
However, this goes against the regulations governing ring final circuits, good workmanship and proper design.
Only accessories, not appliances, should be connected on a ring.
It would (only) be unsafe with regard to the loading of the ring - both balance and total.
The spur itself would be fine.
It doesn't need to carry 32A for a 16A oven; it just has to comply regarding fault current for a 32A MCB.as long as the cable to the spur is big enough to carry 32A.
The basics.What am I missing?
It is just wrong.