Now I have the book in front of me, I thought 433.3.1 was closer to 433.1.103 than it actually is. The key difference being how it regulates overload current, with .103 allowing overload current for "not long" periods.
That surely makes reasonable sense, particularly if, as I suggested before, one regards 'a long period' as being about 1 hour. With any circuit other than a ring, there is the requirement that I
n ≤ I
z, which means that the cable cannot be subjected to more than 1.45I
n for more than an hour - and it seems that the 1.45 times the tabulated CCC (I
z) figures we use is deemed to be acceptable/safe for up to an hour.
With a ring, since I
z may appreciably exceed I
z that 'automatically OK' situation afforded by the MCB is no longer present - so it is down to the designer to make an assessment/judgement about whether an appreciable 'overload' of the cable is likely to arise 'for a long time' (say, more than about 1 hour).
So, we have a conundrum. Do we stick rigidly to 433.1.103 or look towards allowing those "not long" overloads in a circuit otherwise satisfied by 433.3.1? We've all been in the discussion about the slightly overloaded 43A shower on the 40A MCB. Would those electricians see this as any different?
As above, I think the designer input/judgement (particularly that involving the judgement abou 'not likely to be exceeded for a long time) arises specifically in relation to the ring final (because I
n > I
z, so that one does not have the 'deemed to always be safe', regardless of load, situation), and does not really apply to any other type of circuit. That's how I see it, anyway!
Kind Regards, John