Condensing Boiler Efficiency
If all the Water Vapour condenses in the boiler, then the boiler is working as efficiently as it can. (Presumably the manufacturer quoted efficiency)
This is a can of worms.
In central heating mode the boiler cannot condense all the water vapour if the temperature of the water returning from the radiators is above the dew point temperature. In most houses except for the first few minutes of heating the return water temperature is above dew point temperature
For domestic water heating a combi boiler could be fully condensing as the water supply is well below the dew point temperature. However the design of most domestic combi boilers is such that the domestic hot water is heated in a secondary heat exchanger which is heated by the water used to heat the radiators but diverted from the radiators to feed the secondary heat exchanger. Hence the heat exchanger heated by the combustion does not receive the supply water ( below dew point temperature ) but instead receives water returning from the secondary heat exchanger. This is likely to be above dew point temperature.
The test rig used to "prove" the claimed efficiency may be rather different from the real life situation where the boiler is actually installed.
1 cubic metre of natural gas will in "theory" produce 1 litre of condensate
afaik ??
basically there are 2 types of heat (boilers)
1 = sensible heat . which is heat that can be sensed by the boiler.
2= latent heat. latent comes from the latin word (I think ?) Latarre :cool: which means hidden . So latent heat is hidden heat.
A standard efficiency boiler can only extract sensible heat
a condenser is able to extract both types. latent heat via flue heat recovery.
(dunno if the above is relevant to the O.P but I just thought I would mention it :))
1 Kw of energy will raise the temp of 1 litre of water by Hmmm forgot is it 5 degs c ??????o_O
Now when you run a new high efficient boiler,you have to have a high return temp because
if you don't you can reach what is called the dew point.this is when you get condensation forming in the combustion chamber,now being that this dew would be acidic this can cause corrosion,which is why the high return temp is required to stop this,so with the higher temp there is reason to think
that the higher the temp then probably you would get less condensate.
Eh????
I think you are getting confused with the standard efficiency boilers whereby low return temperatures caused premature failure due to back end rot........
Transam it's more like 1.465 litres condesate per cu m methane. Latent heat is released when the molecules in the vapour condense. If they condense in the flue the heat is not transferred to system water. Approx .9kw latent heat potentially available per cu m but you'd be doing well to get between .2 and .5 kw per cu m. manufacturers figures are just that; figures. Volkswagen operate a test facility for boiler operation.
But in a concentric flue some of that heat might be recovered in warming the air being taking into the combustion chamber
Yes, I understand Viessmann use this arguement but the air usually enters a combustion box before mixing with fuel and entering the chamber. I look at it differently, it cools the warmer ambient temp in the box just not as much. It's all miniscule amounts anyway.
A finned stainless steel separator in the flue could recover a lot of the heat from the water vapour. But probably not cost effective in a domestic boiler
but if it reduces the temperature of the flue gases leaving the property then regardless of where the heat energy goes less heat energy has "escaped" from the building.
true in the domestic market
Wow Berny, why didn't someone think of that before?
They did, way way back in the 1960's, and probably even before that. Never the less thank you for thinking I had "invented" the idea but the reality is I am only passing on knowledge I had aquired before even the internet was invented.