Tipper, I trust thats made it clearer! I've given up the will to live. 20/25% will achieve the results you are after.
The return temperature needs to be below the dew point for natural gas, which is approximately 57C but, to be on the safe side let's assume 55C. So the system needs to be designed so that under worst conditions (-1C or lower) the boiler is still able to condense.Again this idea that there is some "ideal" operating temperature for a modern (condensing I presume) boiler. A typical boiler is 3-4% more efficient at 70/50C than at 80/60C and another 3-4% better at 50/30C.
The return temperature needs to be below the dew point for natural gas, which is approximately 57C but, to be on the safe side let's assume 55C. So the system needs to be designed so that under worst conditions (-1C or lower) the boiler is still able to condense.Again this idea that there is some "ideal" operating temperature for a modern (condensing I presume) boiler. A typical boiler is 3-4% more efficient at 70/50C than at 80/60C and another 3-4% better at 50/30C.
I agree that a boiler's efficiency increases as the flow gas temperature decreases because the ratio between the actual volume of condensate in a condensing boiler and the theoretically possible volume of condensate increases as the flue gas temperature drops.
So if the boiler temperature, and consequently the flue gas temperature, reduces as the outside temperature increases more condensate will be available to convert to useful energy and the boiler efficiency will increase.
I suspect that the plume of steam emanating from a condensing boiler flue is the water vapour which has not been converted into useful energy.
Why do rads need to be over-sized at all for the boiler to condense at its best? I thought the more ch water to heat up the longer the boiler must stay on to bring the ch water and room temperatures to a set temperature
Ha, you got me! I finally found your bit of message hiding inside the quoteWhy do rads need to be over-sized at all for the boiler to condense at its best? I thought the more ch water to heat up the longer the boiler must stay on to bring the ch water and room temperatures to a set temperature
Absolutely. I'm sure more than one installer has proudly pointed their customer to a huge plume as evidence of efficient condensing when in fact it is the opposite. Every bit of water vapour you see is wasted energy, and a boiler "fully condensing" emits very little visible water vapour.I suspect that the plume of steam emanating from a condensing boiler flue is the water vapour which has not been converted into useful energy.
Ha, you got me! I finally found your bit of message hiding inside the quoWhy do rads need to be over-sized at all for the boiler to condense at its best? I thought the more ch water to heat up the longer the boiler must stay on to bring the ch water and room temperatures to a set temperature
The reason for "over-sizing" is because the flow temperature should be as low as possible for best condensing, but conventionally sized radiators will not output enough heat at a low flow temperature. It isn't really an issue of how much water is inside the radiators, although that is another issue which might be worth talking about. You can just as effectively increase output by adding fins without making the radiator contain more water. Conventional sized radiators will also very often not output enough heat to allow a 20C temperature drop even at a low pump setting, which isn't ideal for the boiler.
So you will have to whack up the flow temperature in cold weather to get enough heat into your rooms, then the return temperature will be near or above the dewpoint and you will get little or no condensing. You may even have to whack up the flow temperature to achieve the 20C drop. Quite easy to run at 90C/70C even with conventional sized radiators but that sort of defeats the object
Long ago sizing was for 60C above ambient, so in practice about 85C with a 11C or 12C temperature drop (to 75C for an average of 80C over the whole radiator). More recently, radiators seem to be sized to run at 50C above ambient which still means 75C with an 11C drop, or 80C with a 20C which isn't even starting to condense.
So ianniann are you saying that it is impossible to have a desired room temperature ( say 21 degrees) in winter while making the most of a condensing boiler?
Absolutely. I'm sure more than one installer has proudly pointed their customer to a huge plume as evidence of efficient condensing when in fact it is the opposite. Every bit of water vapour you see is wasted energy, and a boiler "fully condensing" emits very little visible water vapour.I suspect that the plume of steam emanating from a condensing boiler flue is the water vapour which has not been converted into useful energy.
And, no ianniann is not saying that. If you want the system to condense in winter the system has to be designed so it will condense.So ianniann are you saying that it is impossible to have a desired room temperature ( say 21 degrees) in winter while making the most of a condensing boiler?Ha, you got me! I finally found your bit of message hiding inside the quoWhy do rads need to be over-sized at all for the boiler to condense at its best? I thought the more ch water to heat up the longer the boiler must stay on to bring the ch water and room temperatures to a set temperature
etc etc
There's no "seem" about it. BS EN 442 states that the output of a rad must be measured at 75C flow, 65C return and 20C room temperature. The connections have to be top and bottom, same end.ianniann said:More recently, radiators seem to be sized to run at 50C above ambient which still means 75C with an 11C drop, or 80C with a 20C which isn't even starting to condense.
It's certainly possible although I suspect a fairly high proportion of people don't do it. My conventional radiators run just fine with the boiler set at 60C, so almost whatever the return there will be some condensing. The return typically runs at between 45C and 50C depending how many radiators are open at the time. Luckily, the room stat is in a large open plan area with four double radiators so the boiler is never stuck on driving through a tiny hall radiator that is little more than a bypass while the TRVs on all the other radiators are shut off.So ianniann are you saying that it is impossible to have a desired room temperature ( say 21 degrees) in winter while making the most of a condensing boiler?
NO!! It's the return temperature which has to be below the dew point temperature of natural gas. You could have the flow temperature at 90C if you wanted, provided the return is below dew point (approx 57C).You need the flow temperature below 53C for full condensation on natural gas.
And where did this advice come from?Current advice is that you do not need to oversize rads when you fit weather comp.