What he said!!Why have all these LGBTQABF RCDs appeared since I retired?
What he said!!Why have all these LGBTQABF RCDs appeared since I retired?
I've offered my suggestion of at least a partial answer!What he said!!
.... I need to know more about the sort of 'fail' (when in situ) you are talking about. Are you perhaps merely talking about it tripping with too low a current (on a ramp test)? ........ before I can answer that, I need to know what sort of 'fail' (when tested in situ) you are talking about - since that will determine my answer (as I said, "there are so many possible situations").
Do you mean that? I am not aware of any minimum trip time for an RCD (hence do not know what 'too early' means). Can you perhaps clarify?IME, the failures are either a no-trip situation, or a trip outside the required time-frame, be that too late or too early.
Fair enough, but what exactly is it you are now describing as the "half times test"?Sorry, don't know what I was thinking... I meant the half times test. Because I had "times" in my head, maybe.
I would quess he means the 1/2 current test 15ma where it should not trip at all, sometimes in life it does trip when tested so i quess thats what he means by too "early"Fair enough, but what exactly is it you are now describing as the "half times test"?
Kind Regards, John
That was indeed the nearest I could think of as to what he might have meant but, if that were what he intended, it would presumably mean that, by now talking of "half times test", he was again making the same mistake of which he said (in the same post!):I would quess he means the 1/2 current test 15ma where it should not trip at all, sometimes in life it does trip when tested so i quess thats what he means by too "early"
... Because I had "times" in my head, maybe.
I have to say that I would be very suspicious and nervous about any item of test equipment which behaved like that!The testers we use at work sometimes trip Rcds purely when you touch the probes onto the Rcd, dont know why
IME, the failures are either a no-trip situation, or a trip outside the required time-frame, be that too late or too early. .... The half times test was the one I was thinking about when writing earlier.
Per above-discussion confusion (mainly on my part), I think I've now worked out what you meant by the "half times test" (and "tripping too early") - namely the situation in which the RCD tripped at or below 0.5 x IΔn (i.e. ≤15 mA for a 30 mA device) - is that correct?Sorry, don't know what I was thinking... I meant the half times test. Because I had "times" in my head, maybe.
OK, but (if you were successful) you would then end up with a device which tested satisfactorily 'in situ' (with loads connected), wouldn't you? If so, then I suppose that most people (probably including myself) would call that a 'pass'.As I previously explained, if I experienced the first, I would operate the mechanism several times and invariably that would free the mechanism and a retest would be within spec. Ditto for late-tripping RCDs.
The testers we use at work sometimes trip Rcds purely when you touch the probes onto the Rcd, dont know why
I have to say that I would be very suspicious and nervous about any item of test equipment which behaved like that!
I'm not doubting what you told us but am surprised (and a little concerned) and, like you, have to wonder about the explanation.Clipped on the Earth , prodded the N and the second the L was prodded. before the Button was operated, the Rcbo tripped. I tried the tester on 3 other Rcbos in the same board and the same happened. Baffles me why it does it, I wondered if it could be a voltage N to E causing it, so next time if it happens i may measure it. At least 1 other engineer with similar tester has experienced it.
As I've said/implied, for what it's worth that is what I would do, BUT ....Maybe its wrong but like Securespark, due to the type of boards we work on, for safety reasons i often test at the socket first and if that fails, then do the Rcbo in isolation ....
As I've said, my personally view is that this is crucially dependent upon the the nature of the 'fail' when tested at a socket. As I've said, if it 'fails' only because it trips with a test current less than 0.5 x IΔn (tripping time being OK), but 'passes' when the device is tested 'in isolation', then the 'on-load fail' is almost always going to be due to L-E 'leaks' due to connected loads - so, as you say, in most senses that is 'fine'. Having said that, the owner of the installation should presumably be 'warned' (maybe with some recommendations about loads, and distribution thereof), particularly if (when tested at a socket) it trips at well below 0.5 x IΔn - since there will then be a high risk of 'nuisance trips'..... and if that passes then fine .... if it finally passes in isolation, im happy with that ...
Isn't it extremely unlikely that 'testing at the RCBO' will produce any different results from 'testing at the socket', if all the same loads remain connected to the circuit? Am I missing something?... it passed the first tests but failed the 5 times test twice when tested at the socket, which as we do commercial stuff, was aprox 50 metres from the board. .... due to this like securespark i opted to go test at the Rcbo, as usual like most pubs, the Db was a mess and jammed pack, it was unsafe to disconnect the load due to the wires buried deep at the rear.