I have received a lot of good ideas/advice and would like to summarise my options. I still think I have 2 problems - firstly a 10 year problem from when the system was fitted ie had to regularly bleed the radiators. This was a new house and so the house builder put some inhibitor in the system which reduced the amount of air but not completely. 5 years ago the heat exchanger failed and then 4 months ago the pump was replaced - the old pump worked perfectly fine but kept tripping out the mains RCD. After replacing the pump that is when the sizzling water noises started and only present when the boiler is at full temperature ( stat set at about 2.5 ) and lasts for up to a minute - although some of that time the boiler is off but I presume the hot water is still on its way to the pump.
Although not everyone is convinced combined feed & vent will work - I feel I have to give it a go. My next door neighbour's house is identical to mine with same heating system except his feed pipe runs 50 mm parallel to the vent pipe. This then t's into the short horizontal pipe above the pump before after another 70 mm it connects to the pump pipe inlet with an elbow. He does not have any air problems
Agile's post looks the preferred option and after digging through the boiler manual they actually show this as a typical layout
Yesterday though I thought I would have ago at implementing a version of combined feed & vent option offered by twgas
I have temporarily removed the vent pipe by disconnecting compression coupling above t and capping it several inches above - no vent at this time and I did not change the 15mm feed pipe at this stage. The method in my madness was it was simple to implement just emptied the tank and ran off a pint or two of water before installing the temporary cap - 10 min job. Bled the system eventually - I now understand Gasguru post of difficulty of bleeding the system in this configuration. On start up the pump is fairly noisy for a couple of seconds. Could this be due to the air pocket that could exist in the cap.
Sizzling water noises again appeared after system got up to heat and I ran the system for 6 hours. This morning bled the radiators - 2 emiited a little air upstairs and one downstairs. The amount of air released was considerably less than previous days so I am thinking that going to combined set up would work.
I still have the sizzling water noises - very noticable around the pump and the pipework in the airing cupboard. The noisee does not appear to be in the pipes around the boiler.
So I am now thinking that problem could be resolved by cowley's
Comments would be greatly appreciated
Although not everyone is convinced combined feed & vent will work - I feel I have to give it a go. My next door neighbour's house is identical to mine with same heating system except his feed pipe runs 50 mm parallel to the vent pipe. This then t's into the short horizontal pipe above the pump before after another 70 mm it connects to the pump pipe inlet with an elbow. He does not have any air problems
Agile's post looks the preferred option and after digging through the boiler manual they actually show this as a typical layout
Converting to a combined feed and vent will normally solve any problems.
You could do this within your room will be OK but do use 15 mm for the feed.
Tony
Yesterday though I thought I would have ago at implementing a version of combined feed & vent option offered by twgas
cold feed needs to be in 22mm from tank to system and do away with open vent. easiest way is to cap 15mm and drill and fit a new 22mm tank connector. enlarging a hole in a tank is more difficult than fitting a new one.
I have temporarily removed the vent pipe by disconnecting compression coupling above t and capping it several inches above - no vent at this time and I did not change the 15mm feed pipe at this stage. The method in my madness was it was simple to implement just emptied the tank and ran off a pint or two of water before installing the temporary cap - 10 min job. Bled the system eventually - I now understand Gasguru post of difficulty of bleeding the system in this configuration. On start up the pump is fairly noisy for a couple of seconds. Could this be due to the air pocket that could exist in the cap.
Sizzling water noises again appeared after system got up to heat and I ran the system for 6 hours. This morning bled the radiators - 2 emiited a little air upstairs and one downstairs. The amount of air released was considerably less than previous days so I am thinking that going to combined set up would work.
I still have the sizzling water noises - very noticable around the pump and the pipework in the airing cupboard. The noisee does not appear to be in the pipes around the boiler.
So I am now thinking that problem could be resolved by cowley's
Add fernox/sentinal or other as you prefer to system as per instructions/quantities etc and circulate through boiler,primary flow & returns hot water circuit rather than heating circuit not the best time of year to do this, or power flush through this circuit.
Comments would be greatly appreciated