So the cpc in t&e is sized to be sufficient not to melt before the MCB trips.
We can get away with unfused spurs in rfcs because of the single accessory special dispensation (i don't believe there's a normal reg that allows it for a socket outlet is there?)
If the load was hard wired and unlikely to overload eg water heater we could also have a 2.5 cable, we could also take account of the special dispensation i think?
However the cpc in the cable is only 1.5mm therefore wouldnt comply regarding minimum cpc size. The minimum may up to around 1.8 for a 32a mcb.
Is that just classed as a fudge to allow old rfcs, or is that a more general exception?
We can get away with unfused spurs in rfcs because of the single accessory special dispensation (i don't believe there's a normal reg that allows it for a socket outlet is there?)
If the load was hard wired and unlikely to overload eg water heater we could also have a 2.5 cable, we could also take account of the special dispensation i think?
However the cpc in the cable is only 1.5mm therefore wouldnt comply regarding minimum cpc size. The minimum may up to around 1.8 for a 32a mcb.
Is that just classed as a fudge to allow old rfcs, or is that a more general exception?