How about - because 433.1.204 specifically mentions them along with other OPDs?
It lists all acceptable OPDs.
It makes as much sense to say that therefore 433.1.204 is still written for 3036 fuses than it does to say it is still written for any other type of device.
Interesting to note though that BS3871 devices are not allowed.
Therefore, if the circuit is compliant with 3036s then it is excessive for MCBs.
That applies to all circuits because of the nature of 3036s, not because of the circuit topology.
Because MCBs have less onerous circuit design requirements than 3036s.
I
z has to be 20A. It doesn't matter what the type of device is, it has to be 20A. The less onerous requirements of MCBs vs 3036s means that you can use 2.5mm² cable with MCBs when you might not with fuses due to installation method.
It's no different from any circuit where you need a given I
z - if your device is a 3036 fuse then sometimes you'll need a larger cable than you would if it were an MCB.
It's all very well laying out the requirements but then to negate them by having to add "Subject to it meeting the minimum csa requirement as well" would appear to render the requirements pointless.
Don't shoot the messenger. 433.1.204 imposes a minimum csa. It just does. I understand why just as much as I understand Table 52.3, which equally "renders pointless"
Ib ≤
In ≤
Iz requirements.
Aren't you confusing two separate things?
No, because I have no evidence that it is anything more than coincidence.
The 20A is 66.7% of the 30A (3036) rating
It's ⅔ of any 30A device, irrespective of any device characteristics which affect cable ratings.
and the need for 2.5mm² (with 27A CCC) is because of the 3036 0.725 derating.
Yes,
if that factor applies. And the need for 2.5mm² (with 27A CCC) is because of the derating which has to be applied for Reference Method A if that applies.
It does, though, mean a 40A MCB would be satisfactory on a ring.
It wouldn't, because BS 1363 accessories are not rated to have 27A in the cable they are connected to,
20A
is ⅔ of 30A. But 20A was not chosen
because it is.
Exactly. So I am correct.
I point out that you need an
Iz of ≥ 20A, and that that involves considering installation method and all the other applicable rating factors (of which C
f is only one), and you say that.
I'm not sure what you think I've shown you to be correct about, but it certainly isn't your basic premise that 433.1.204 is still written for 3036 fuses.
It isn't, it's written for ring final circuits wired using cables with an
Iz of ≥ 20A, i.e. cables with a CCC that takes into account installation method and C
a, C
c, C
d, C
f, C
g, C
i, & C
s.
Exhibit B: Table 52.3. Sometimes the regulations impose a minimum csa.
Although for 32A MCBs shouldn't it be a CCC of (32*66.7%) 21.33A?
No, it should be 20A, because that is what has been required for the last 16 years.