The RCBO / RCD might not trip, but there is also the issue of the protective conductor current in the circuit:
http://electrical.theiet.org/wiring-matters/26/5437-earthing.cfm?type=pdf
That's true, but I never have really understood the requirements of 543.7 as regards 'high integrity earthing'.
The main ways (certainly the main ways likely to be implemented in a domestic setting) of satisfying the requirement for 'high integrity earthing' is for the circuit to have a CPC of ≥10mm², two CPCs totalling ≥10mm² or a mechanically-protected ≥4mm² CPC. That really makes little sense to me. The resistance/impedance of the CPC is essentially irrelevant - even 30mA leakage through a CPC with a ('ridiculously high') resistance of 10Ω would only raise the potential of the CPC and any connected exposed-c-ps by 0.3V. Even if the circuit were not RCD protected and had a (ridiculous, in normal functioning) leakage of 1A, the potential would only rise by 10V !
The actual
real risk is that the CPC might somehow become
disconnected from earth, in which case the 'leakage currents' could represent a real risk of electric shock (if one could find something at earth potential to touch simultaneously). However, I do no see that a 10mm² CPC, or a mechanically-protected 4mm² CPC, is significantly less likely to become 'disconnected from earth' than is a 1.5mm² one, can you? Am I missing something?
Furthermore, if there were a "disconnection from earth" between the earth bar of the CU/DB and 'earth', then the same problem would exist in
all circuits in the installation, yet requirements for 'high integrity earthing' would only apply to circuits with a known/suspected high leakage.
Hence, whilst I understand the potential risks being addressed, I really don't see that the regs address them significantly or satisfactorily - do you? Again, am I missing something?
In the domestic setting, the most important thing is that the circuit is RCD/RCBO-protected. Such a device would at least operate if there were a leakage current (even if through a human being, rather than CPC) of, at most, 30mA (in practice usually apprecially less).
Kind Regards, John