OK.
So do you ignore that one too, and install ring finals without the cpc being in a ring? If not, why not?
I think we've done this one to death. 543.7.2.201 says "
... shall be provided with a high integrity protective conductor connection complying with 543.7.1. The following arrangements of the final circuit are acceptable: (i) A ring final circuit with A ring protective conductor...". Is that not saying that "a ring final circuit with
A ring protective conductor" is one acceptable way of achgieving the required compliance with 543.7.1?[/quote]
Yes.
But have you not spotted that "complying with 543.7.1" means "complying with 543.7.1.203"?
If so, which of the high integrity protective conductor connection complying with 543.7.1.203 do you want to go for for?
One consisting of a single protective conductor having a csa of not less than 10mm²?
Or one consisting of a single protective conductor having a csa of not less than 4mm² with added mechanical protection?
Those are the only two ways
(apart from (iv) and (v)) in which "a ring final circuit with
A ring protective conductor" will comply with 543.7.1.
I think we've reached the point at which I have to say that I don't really care what the regulations precisely say.
Dear God.
Just think of how much time we could all have saved if you had adopted that attitude from the beginning, instead of going on for page after page after page arguing and twisting and inventing and accusing me of doing things I wasn't doing but you were, all of it, all of it, because I was trying to get you to recognise what the regulations precisely say.
It was always about nothing except what the regulations
actually say, and if you don't care then it was shameful of you to ever join in.
BAS seems to be arguing for the sake of it!
Goodbye - I am not going to waste another minute of my time discussing this any more with you.