15 double sockets on 70 meters of 2.5mm t/e is what i am try work out
on a kitchen and utility room
15 x 2 x 13amps = 390amps. Easy!
then 390A x 'diversity factor' = 32A, magic
If you are using a ring final on a 32A mcb, there is guidance to suggest that this circuit should serve no more than 100m^2 of floor space.
I guess this limitation serves to replace any diversity calculations, perhaps using the thought that you would only expect to see a certain amount of appliances in use in a limited space, in 'normal' circumstances.
Also, if you embrace the whole spirit of using 'standard circuits' and follow the guidance that fixed appliances over 2kW should be supplied by its own dedicated radial circuit, then its not very likely that you will even see a ring final pulling near 32A
But of course, this is just 'guidance' to a non-mandatory set of regulations.
(just thought id drop that little chestnut in, for a laugh - cue uk schuko installers and wannabe lawyers)
It is still the responsibilty of the designer to take a view on the intended use of the installation and install something appropriate.
IMO, ring final circuits are becoming less practical due to the greater requiremnen for circuit segregation.
Radials - its the future!