Does the magnetic part of a MCB matter when using a RCD?
The first thing I look at is the RCBO which come in type B or C so one would consider yes it does.
Although the magnetic part is required where the loop impedance is below the threshold the question is does the loop impedance need to be low enough to trip the magnetic part?
For different systems we see a range of maximum disconnection times from 40 ms, (30 ma RCD) 70 ms,(RCD) 0.2 s,(Table 41.1) 0.4 s, (Table 41.2/3) 5 s (Table 41.4) but these are it would seem for line – earth faults which is covered by the RCD today. At around 10 seconds depending on the type the thermal part of the MCB takes over so only if it needs to trip in less than 10 seconds does one need the magnetic part need to work.
If answer is yes then we need to measure line – neutral loop impedance yet IET forms do not have a provision for this reading so rarely measured. Thoughts please.
The first thing I look at is the RCBO which come in type B or C so one would consider yes it does.
Although the magnetic part is required where the loop impedance is below the threshold the question is does the loop impedance need to be low enough to trip the magnetic part?
For different systems we see a range of maximum disconnection times from 40 ms, (30 ma RCD) 70 ms,(RCD) 0.2 s,(Table 41.1) 0.4 s, (Table 41.2/3) 5 s (Table 41.4) but these are it would seem for line – earth faults which is covered by the RCD today. At around 10 seconds depending on the type the thermal part of the MCB takes over so only if it needs to trip in less than 10 seconds does one need the magnetic part need to work.
If answer is yes then we need to measure line – neutral loop impedance yet IET forms do not have a provision for this reading so rarely measured. Thoughts please.