I read on the other Electrical forum an old discussion about RCD's and American GFI's. In this discussion it was stated that RCD's do not give Overload protection, however I would like to point out that this is wrong, RCD's DO give overload protection, only basic, but it is there.
I hope you never do work for anyone I know. The leakage current is not the load so it does not give any overload protection.
RCD's and Isolators can look very like MCB's and I have seen both used where the guy thought they were giving overload protection. The Loadmaster range of MCB's had one with red operating bar with 100A marked on it which was purely an Isolator but looked very similar to the MCB's
As to DC sensing the "A" type will sense DC but it does need to move through a zero volts in wave form to work. The "AC" type will not work with DC. There are specials that will work with pure DC but these are very special.
There are many types of RCD / RCBO from active to passive to multi-pole switching and single-pole switching. They will be marked with a number of ratings. The let-through amps they can handle often around the 4700 amp. The working amps they can handle for example 63A and the tripping amps for example 0.03A and the time to trip for example under 40ms or S type. Some will allow these setting to be altered and they can be in three sections the control unit with time and amp pots for setting the current transformer and the mounded breaker used to open the circuit in event of a fault.
When combined as with last example with a moulded or miniature breaker then they will also have another two devices a thermal overload and a magnetic overload.
However passive RCD's do not fail safe. It does not matter if fitted to moulded breaker or a single pole switching RCBO as used in domestic if the voltage falls below a threshold or a wire becomes disconnected they may fail to work. The test button only tests the mechanics of the device and it needs a special meter to test the time they take to trip.
The domestic single pole RCBO has a draw back in that it does not open all live conductors only the line conductor is opened as a result their use is restricted to a selected earthing arrangement and can't be used in all premises.
Some RCBO are sold in two parts and there must be an issue there where they can be assembled wrong and even when supplied as one using heavy cables and incorrect buss bars can warp the case preventing them from working so all RCD devices should be tested after fitting and I don't mean the test button.