Twisting is/was never acceptable.(I used Wago's instead of twisting cables etc)
The RCD should be tested at the consumer unit with loads disconnected.With regards to RCD disconnect times, I measured at the furthest outlet on the ring
The higher figure of each test is recorded.and quoted the higher 180 degree phase figures (I didn't know whether it's supposed to be quoted at 0 or 180 so went with the highest).
It depends at which point in the cycle you start the test.If anyone knows why 180 degree phase figures are a bit higher, I'd be interested to know (being a layman, I've no idea).
The resistance for the larger bonding cable to the kitchen came out 1.48 Ohms (probably in the regions of 10-15m of cable).
That is wrong - it's far too high. Assuming it's 10mm wire, actual resistance should be around 0.02 ohmsThe resistance for the larger bonding cable to the kitchen came out 1.48 Ohms (probably in the regions of 10-15m of cable).
On a ring circuit, the Zs value should be the same at every outlet.The Zs values increased the further I got from the consumer unit in quite a consistent fashion to give the maximum 0.62 Ohms at the furthest outlet.
Thanks for the replies. I took the previous version of the minor works down as I realised a few things were wrong. The hawk eyed among you obviously spotted it too quickly!
I can't really tell.I wonder if anyone can please identify the size of the green/yellow bonding cable (pics show this at the meter box and the other end attached to pipework under the sink) and the smaller green earthing cable in the meter box?
Just because it is black does not mean you can call it a neutral lead.I'm assuming the green/yellow sticker on the neutral lead means it's been used a return earth?
If that one is 6mm² then the others must be 10mm².The slimmer green earthing cable goes straight through my meter box and terminates in my upstairs neighbours meter box earthing terminal.
No, they should be negligible, <0.05Ω.I took a reading of the resistance between the consumer unit end and the end at this meter box and it was 0.18 Ohms - does this sound acceptable? The resistance for the larger bonding cable to the kitchen came out 1.48 Ohms (probably in the regions of 10-15m of cable).
I would suspect the meter.Regarding the Zs value, I took this at the furthest outlet on the ring circuit. I actually went round and measured it at every outlet - that for the new double socket the fused spur is taken off (which is very close to the consumer unit just the other side of the kitchen wall) came in as 0.27 Ohms. The Zs values increased the further I got from the consumer unit in quite a consistent fashion to give the maximum 0.62 Ohms at the furthest outlet.
Yes, that sounds fine but there may be things on the circuit which could affect the times and it is the actual device that you are testing.Not a lot I can do about remeasuring RCD times as the kits gone back, I think I thought measure at the furthest outlet on the ring because that's the furthest distance the current has to travel to trip the RCD. Still, I measured the times at all the outlets on the ring and they were all well within limits (and very similar values), so I'm happy that it's working as it should.
They would comment on it but it is fine.One thing I did find - the lights and immersion are only on an MCB, not an RCD and MCB. I suspect if I got a PIR done professionally they'd say do something about that.
That couldn't possibly be true. One socket could be right next to the CU, with an (R1+R2) of virtually zero, whilst another might be in the middle of a 100m long ring, hence with an (R1+R2) corresponding to two 50m long cables in parallel (i.e. fairly 'high'). Zs is obviously just (R1+R2) plus Ze.On a ring circuit, the Zs value should be the same at every outlet.
With a ring, (R1+R2) increases (along both 'arms') non-linearly from zero at the CU to a maximum at the middle of the ring (see illustrative graph below). With an unbranching radial, (R1+R2) will increase linearly from CU to the far end. Again, Zs is obviously just (R1+R2) plus Ze.Increasing as you get further away from the origin indicates it is a radial, or a ring which has been broken somewhere.
It isn't, clearly a mistake.That couldn't possibly be true.On a ring circuit, the Zs value should be the same at every outlet.