Hi Im in the process of installing a texecom system with no previous experience of them and trying to do some testing as I go .Installed all the pir's with EOL wiring which I think are OK.
Now at the stage of doing the door contacts.What I have done is bridge the reed switch contacts with a 4.7k resistor and from one side installed a 2.2k resistor to a spare terminal which I shall connect 1 of the pair of alarm wires,the other wire to the other end of the reed switch.
The readings I am getting on the alarm pair is 6.8K with the door open and 2.2K with the door closed ,Can someone confirm if this is correct before I do the others Thanks