Yeah, the original thread was a slightly different problem which I have now solved.
But the new problem could be related to the old. How did you solve the old problem?
The issue now is that the light on the SCR comes on and the boiler fires for no apparent reason, even if I take the batteries out of the +3rf in the living room.
You need to find out why the light is coming on. (Obvious, I know.
)
The light must be connected to terminal 3 of the SCR so it only lights when the internal switch closes, connecting 1 to 3. So you should get: L feeds 1, which feeds 3 (via the internal switch), which feeds boiler R.
Now, what would happen if something in the boiler reversed the process (Don't forget that the boiler has a permanent supply): Boiler R feeds 3. The green light would still come on, but the switch in the SCR would be open.
Disconnect the link between L and 1 on the SCR backplate. You will still get you hot water, but you should not get any heating. If the heating still comes on at random times, the fault must be in the boiler. If the problem goes away (you get cold
), there must be a fault in the SCR.
If you still suspect a faulty SCR, reconnect the link between L and 1 and disconnect the wire to 3. You won't get any heating, but you will be able to check if the SCR still comes on when it shouldn't.
PS Take the batteries out of the control unit to eliminate that source of the problem.