then the ELI is well within limits for TT (460 max).
It is actually 500 Ohms max. if you take Uo as 230v.
But either way with anything above 200 it must be ascertained that this is a stable reading and not likely to increase as ground conditions change.
To the op:-
I suggest you seek the services of a competant Electrician
The supply voltage doesn't make any difference, the calculation is on a maximum permissable touch voltage of 50v hence the max Zs for a 100mA RCD is 50v/0.1A=500 ohms
I'll 2nd the need to contact a competent electrician.
From the description he has a TN not a TT system. And only one socket tested likely it seems with one of these and the guy has a problem understanding what Zs and Ze is.
To get technical does not help him.
His options are either buy himself one of the cheap testers at £34.95 not too expensive and remove faulty sockets and physical test the earths. However these testers only test Zs and although one could make adaptors to test Ze with his admitted knowledge rather a dangerous idea. Also this does not give him the bit of paper he needs to help sell his house.
So it would seem his only option in real terms is to pay an electrician and since selling house he wants one with a scheme logo on his paper work to do a PIR (Periodic inspection Report) in the same way as he had the gas done. And at same time correct any minor faults. When I say minor I refer to amount of work not the amount of danger.
We know the lack of RCD's will be high lighted but if all faults are code 4 then that's all he needs to sell house. Even some code 2 faults my not be too bad but at the moment the fault highlighted is something that if I was buying the house I would want to know more.
In some ways when selling the house it would have been better not to have known. But now if someone should plug in a faulty bit of equipment into that socket and get electrocuted the investigation would show he was aware. So he must either rectify or pass on the information to the new occupiers.
I suppose he could be sneaky and state it is know the electrics don't comply with current regulations and a full PIR is recommended. I watched the political TV series last night. And that way he has said it is faulty without saying how bad it is. But I couldn't do that even if it did get me out of a hole.
So forget Ze, Zs, TN, TT lets try to give the man some advise he can use. To me that is still get some one in to do the work!