As said in the main equipment in the garden is class II so no earth, items used outside which are larger, narrow boat, caravan for example TN-C-S supply is banned, electric cars can have a special arrangement where if the voltage is not between 207 and 253 volt it auto disconnects first lives then earth, this is an odd one out, not seen on anything but EV charging.
The problem is two earths at a diffrent voltage, and the distance between them so the gradient of voltage, to use a caravan fire regulations means at least 2.7 meters from a building, so gradent likely shallow enough, but in storage my father-in-laws caravan was less than a meter from the gas and electric meter, and on concrete, so used the TN-C-S supply as could touch both electric meter and caravan together.
A radio ham friend has his shack around 4 meters from house, and the electrician who wired it used a 4 mm earth wire between the two, and bonded it to the radio earth bar, which in turn connected to 4 earth rods one each corner of garden and earth tape between them.
When road works broke the PEN, he noted plastic melting off 4 mm earth wire, so turned off all power, this made no difference as earth not through isolator so the 4 mm earth wire reduced to copper balls, the whole estate was trying to earth through his earth.
Ohms law means 40Ω earth will at 400 volt carry 10 amp, so a 40Ω earth electrode and wire must carry 10 amp to be safe, so you need the measure the ELI of the lamp post, and work out the prospective short circuit current, it is not a simple earth or don't earth, connecting the wrong side of a gas supply electrical isolator block to earth has caused fires, normally blamed on copper theft, but as with most accidents more than one cause.
So depends how close to other earthed items, I would normally use TT supply, but depends where it is, there are always exceptions.
The problem is two earths at a diffrent voltage, and the distance between them so the gradient of voltage, to use a caravan fire regulations means at least 2.7 meters from a building, so gradent likely shallow enough, but in storage my father-in-laws caravan was less than a meter from the gas and electric meter, and on concrete, so used the TN-C-S supply as could touch both electric meter and caravan together.
A radio ham friend has his shack around 4 meters from house, and the electrician who wired it used a 4 mm earth wire between the two, and bonded it to the radio earth bar, which in turn connected to 4 earth rods one each corner of garden and earth tape between them.
When road works broke the PEN, he noted plastic melting off 4 mm earth wire, so turned off all power, this made no difference as earth not through isolator so the 4 mm earth wire reduced to copper balls, the whole estate was trying to earth through his earth.
Ohms law means 40Ω earth will at 400 volt carry 10 amp, so a 40Ω earth electrode and wire must carry 10 amp to be safe, so you need the measure the ELI of the lamp post, and work out the prospective short circuit current, it is not a simple earth or don't earth, connecting the wrong side of a gas supply electrical isolator block to earth has caused fires, normally blamed on copper theft, but as with most accidents more than one cause.
So depends how close to other earthed items, I would normally use TT supply, but depends where it is, there are always exceptions.