I'm sure you understand all this at least as well as I do, so I don't quite understand why you're making such a meal of it. The water (and gas, if they exist) supply pipes are e-c-p's and therefore require Main (Equipotential/Protective) Bonding (MPB) close to where they enter the building. The internal pipework and taps within the building (which may or may not be in electrical continuity with the supply pipes at entry) never require MPB and, under current regs, rarely are required to have any bonding at all (i.e. not Supplementary boding either).If that is the case then they do not require bonding.Internal pipes and taps obviously cannot actually be extraneous conductive parts, as defined in BS7671, since they cannot in themselves be "liable to introduce a potential into the building" (since they are entirely contained within the building).
IIRC, all the op told us was that pipes in the bathroom 'were earthed'. That obviously is not going to be Main Protective Bonding (unless the water supply enters the building in the bathroom). Even if it were, the requirement would be to connect the pipes via a Main Bonding coductor to the MET, not to other pipes or the bath, or even a local CPC! I therefore don't really understand what you are going on about!The OP's pipes are bonded, so we have to assume that they are e-c-ps.
As I said, pipes and taps within a building can never be e-c-ps as defined by the regs (provided that proper MPB is present). Again, you appear to be talking about Main Protective Bonding (since that's the only context in which e-c-p is relevant) to pipework distant from the entry point into the building, which is not a concept of BS7671 under any circumstances.Then if there is no other way for the pipes and taps to introduce a potential they are not e-c-ps and BS 7671 does not require them to be bonded.
See above. You seem to be fixated on extraneous-conductive-parts within a building, which really cannot exist (per BS7671 definition) if MPB is in place. There is no requirement in the regs for multiple MPBs, just in case the primary one fails and thereby renders other pipework liable to introduce a potential.The regulations only result in pipes being connected to the cpcs if the pipes are e-c-ps.If not, why do you regard it as 'crazy' to have the bath so connected, whilst accepting that the regs usually result in that being the case with the taps, pipes and radiators?
If they are not e-c-ps then they do not require bonding, and therefore do not end up connected to the cpcs.
Kid Regards, John.